Discuss Led ceiling Lights - one light Flickers when other is switched ON in the Lighting Forum area at ElectriciansForums.net

Reaction score
0
Hi,
In my room 2 Led round ceiling lights are installed, week ago both were fine, but now when I turn on both lights, one starts flickering, even their emitting light is getting low...

Is it switch problem or LEDs needs replacement?
 
Hi,
In my room 2 Led round ceiling lights are installed, week ago both were fine, but now when I turn on both lights, one starts flickering, even their emitting light is getting low...

Is it switch problem or LEDs needs replacement?
Are they both on the same switch? If so then it's unlikely to be the switch, unless they are wired separately from it and there is a loose connection behind it

Or are you saying one flickers only when the other one is on?

It may well be the LED driver is giving up, which is often built into the light fitting these days so needs a new light fitting. It could also be a loose connection on either live or neutral though.

In either case, it should be less than an hours work for any competent electrician...
 

Reply to Led ceiling Lights - one light Flickers when other is switched ON in the Lighting Forum area at ElectriciansForums.net

Similar Threads

I have purchased spotlights as below, but they are flickering when I dimmed them down to around 15-20%. We have installed 8 x ALUSSO LED Recessed...
Replies
4
Views
1K
Hello all- I hope this is the right place to ask this question. A few weeks ago the LED lights in the kitchen started flickering intermittently...
Replies
2
Views
728
Hi all, Great forum with lots of advice read and greatly received over the years! I have a question here that I am hopeful somebody here can...
Replies
16
Views
1K
I bought a ceiling fan with LED lights. After some time the led lights started flashing when I put them on. Now it does not even jump up anymore...
Replies
0
Views
600
Hello, I'm replacing standard light switches in my hall and landing with touch switches (not smart, just touch on/off) like these from Amazon...
Replies
7
Views
700

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock