Discuss LED Floodlight in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hello.

Just a quick question.

Got 8 140w led floodlights running on a B20 mcb. The lights come on through a mechanical timer but the customer says everytime the timer switches it trips the mcb. But they work fine when the manual switch on the timer is pressed. Can you run LEDs of a manual timer?

Thank you.
 
try a C16 or a C20 curve MCB assuming the Zs complies.
 
LEDs do and the timer might just be the last straw.
 
They are inductive loads all the calcs etc and switching ability including the rating and type of mcb needs calculating with respect to their combined inrush spike....

The mcb is a B type and even though 20amp the time curve is probably your issue to nuisance tripping... i would speculate this has been installed by a domestic sparkie who hasn't done further education with regards to circuit design courses.

My first port of call would be to ring the manufacturers and ask about the peak inrush for 1 fitting then liaise with the mcb's manufacturers with this info and see what max nno' fittings can be put on any one mcb.. once you know this then you design the circuit to eliminate nuisance tripping on inrush.


To give you an idea if this is the issue disconnect half the fittings and try again and also try a C and D type to see if this also stops the tripping if so you need to redesign the circuit if you can't meet Zs values with a C/D trip curve.
 
Hello.

Just a quick question.

Got 8 140w led floodlights running on a B20 mcb. The lights come on through a mechanical timer but the customer says everytime the timer switches it trips the mcb. But they work fine when the manual switch on the timer is pressed. Can you run LEDs of a manual timer?

Thank you.
sounds like a faulty timer as the manual switch will create the same surge, assuming there is one, as the timer switch
 
From what you describe it sounds like a Sangamo timer and only has a clock motor as all switching etc including the over-ride is purely mechanical action, the timer funtion may be closing the contact at a slower rate than the quick snap action of the over-ride button and may create additional spike inrush as if an arc is created due to slower switching.... it would still point to the size of inrush been a key factor... can you confirm the make of time clock?
 

Reply to LED Floodlight in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Total novi e but have wired multiple light switches previously and survived :) I've bought a nice WiFi enabled dinner switch for a new LED...
Replies
11
Views
963
Hello I have some decking lights which to be fair, have been nothing but pain in the bottom since they were installed. Moisture in the lens lamps...
Replies
10
Views
2K
Hello, I've installed a Monsoon Extractor Fan kit today, all is up and running and everything is working with the exception of the LED. When I...
Replies
0
Views
697
Hello all- I hope this is the right place to ask this question. A few weeks ago the LED lights in the kitchen started flickering intermittently...
Replies
2
Views
695
hello all. I am trying to add led strip lights to my boat trailer. I have marine grade submersible lights. I will have them running parallel to...
Replies
3
Views
817

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock