Afternoon all,
New to the site so thanks in advance.
Currently working on a new build, the supply was installed last week (new build) 80a fuse installed, EON installed the meter this week with 100a DP switch. All fitted within the external meter box. I’m looking to run tails, ideally I need to come down from the box approx a meter and then through cavity wall into 100mm trunking into metal CU (RCBO). Full length of tails need to be 4.5m. As above I was aware of the 3m rule unless switched. As there is already the switch by EON, does this account for a switched spur and allow the extra length required?
 
The presence of a switch has no bearing on the length of the tails.

The length of tails that the DNO permit their fuses to be used to protect is 3m, so if you need a cable longer than this to connect to the CU then you need to install a distribution circuit to do this.
 
He means, you might be required to provide your own switch fuse for tails over 3m. Have you enquired with the DNO? Why is the main fuse 80A?
 

Reply to Length of tails in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

On a new build site how/ why are people getting away with installing meter tails over 3metres in length and behind dot and dabbed walls with no...
Replies
7
Views
2K
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Hello again, Was looking at installing yet another dedicated consumer box for my EV charger off the henley blocks and i noticed that a meter...
Replies
11
Views
2K
Hi all. Just a quick one if I may. I am currently about to fit 3 gang smart touch switch at my front door but owing to powering two sets of...
Replies
9
Views
972
We had a new supply installed this week. DNO installed new cut out and fuse externally. Meter operator sent his engineer to move the meter in the...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock