Discuss Light Switch Installation in the DIY Electrical Advice area at ElectriciansForums.net

Reaction score
0
The light already installed can be controlled from the top and the bottom of the stairs and I was advised to buy a 1 gang 2 way switch. The old light switch has 4 terminals but the new one only has 3. My question is where the earth goes as there is no terminal for it on the switch or inside the back box.
 

Attachments

  • 20210921_131036.jpg
    277.2 KB · Views: 19
  • 20210921_131043.jpg
    192.7 KB · Views: 19
Disconnect the short earth tail from the terminal in the back box, leaving the earth wire from the incoming cable still connected.
 
Disconnect the short earth tail from the terminal in the back box, leaving the earth wire from the incoming cable still connected.
Hi Thanks for your reply.

Do you mean I should leave the earth in the u shape where it is and remove the other earth wire that is hanging loose completely
 

Reply to Light Switch Installation in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi, I’m looking to install 3 meross smart switches for 3 lights: entrance switch: only 1 gang but 3 way switch bedroom switch: 2 gang (1 is 1...
Replies
9
Views
395
Hi I want to add a light to my attic. There is a single switch on the landing that I want to change to a double switch and then use it to still...
Replies
24
Views
1K
Hi, in my bedroom i had a 2 gang dimmer that powered 2 set of 3 spot lights and also had passthrough wires to other sockets. Im changing to just...
Replies
2
Views
250
Hello everyone... There are a total of 4 cables entering the junction box at the top of the staircase. Two 12/2 cables are coming in through the...
Replies
1
Views
449
I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
513

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock