Discuss Lighting circuit trips RCD but not MCB, can’t find E-N fault in the Australia area at ElectriciansForums.net

Reaction score
0
Long shot but thought I’d try, have a lighting circuit that trips the RCD as soon as the neutral touches the neutral bar for said RCD. Bypass that and it works fine just on an MCB so would think earth-neutral fault, but doing an IR test between N and E shows as a pass (>99M ohm). So unsure of what to do, any suggestions would he great.
 
Do you have more than one RCD / neutral bar?

It could be on the wrong one. Also background, has this developed as a fault and you now find that isolating/replacing the neutral in its old position explains things, or did you do some work and now it is having trouble?
 
Do you have more than one RCD / neutral bar?

It could be on the wrong one. Also background, has this developed as a fault and you now find that isolating/replacing the neutral in its old position explains things, or did you do some work and now it is having trouble?
There are multiple RCD’s but have traced the neutral and made sure it is on the right bar. The fault has spontaneously happened, client has had no issues up until now and no electrical work has been done recently.
 
It may be that you have a N to N fault.
if there is a link from one N bar to the other being generated by a mistake or fault between circuits it could cause the issues you are having.
 
Hi all, I’m a Melb based homeowner who has a similar issue.
TLDR: How to fault ID - new RCD trips lighting circuit - motion sensor Poss culprit?
Longer version
Solar installer upgraded MCB from ceramic-wire fuses to RCDs.
Ever since then an outdoor lighting circuit (which has motion sensing and runs PAR floods as well as std bayonet fitting) now trips the RCD on the lighting circuit instantly.
Have been looking at water ingress to fittings but all clean and clear - but thinking movement sensor failure may be the issue?
Old fuse never blew, so unlikely a load issue. Also suspect that one light fitting is actually powered from both the problem circuit and another circuit.
1970s home.
Thnx for any advice.
 
Do you have more than one RCD / neutral bar?

It could be on the wrong one. Also background, has this developed as a fault and you now find that isolating/replacing the neutral in its old position explains things, or did you do some work and now it is having trouble?
That's the likely fault
 
take all the neutrals out of all the neural bars (mark them first) puts wagos on each one and power up the offending circuit,any neutrals connected though a load will now become live, i use this technique to upgrade mcbs to rcbos
 

Reply to Lighting circuit trips RCD but not MCB, can’t find E-N fault in the Australia area at ElectriciansForums.net

Similar Threads

I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I'm not sure what's going on with my kitchen light. I've replaced an old 28W CFL fitting with a new 4 x LED GU10 fitting (a cheap one from...
Replies
11
Views
1K
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
921

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock