Discuss Live Earth Reverse in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
29
Hi Guys

So has anybody had this issue as I'm baffled. I've completed an EICR today and all other circuits apart from the ring main were fine. I had no continuity in the ring.

I tested each leg and can see there is a break between a couple of sockets...probably under a Floorboard as between the socket connections we're fine.

Anyway I continued my tests and recommended I come back to check on the break. However I've connected everything up at the board and there tv socket wasn't working...where the break is I'm now getting a Live Earth Reverse (according to my lap tester)

The Live Earth Reverse us literally for 3 sockets, I've checked the sockets and there fine...I didnt actually mess with the connections anyway. All other sockets in the house are fine, these 3 are in the middle. I've checked the board and tge connections are in tge right place and voltages are correct.

Confused.

Andy
 
Which conductors are broken in the ring? All of them or just one?
 
If would make more sense if I was called out to a fault. However I haven't messed with the connections and the 3 sockets worked fine before apparently.

Not sure if running the IR down each leg has caused an issue
 
I'm now getting a Live Earth Reverse (according to my lap tester)

This indication can be caused by a broken neutral especially if there is load connected past the dis that pulls the neutral pin of the tester up to line volts. What the tester then sees is voltage E-N but not L-N, which is the wrong way round so it indicates a reverse connection. I suspect there is a faulty connection in the N that has been disturbed during inspection.
 
I have had something similar, and it was so long ago the details are hazy.
I also had a broken ring.
I wouldn't do it like this now, but at the time I made a 2nd break in the ring (safely wago'd) building a picture of what worked and what didn't. In my case I had "Live and Neutral reversed " between the break I put in and what the break in the CPC that was already there.
In your case I would bet you have a broken Neutral and the tester is confused, they are fairly primitive in their logic.
EDIT cross post with @Lucien, sorry
 
Well using voltage testers can get continuity but my megger doesn't like it so couldn't get an R1. Earth no continuity whatsoever
Sorry - I'm struggling to understand what you're meaning here. Live <> Live = fail? CPC <> CPC = fail as well??
 
Note that when I say a disconnected neutral I mean one that creates an island of sockets with no neutral connection to either leg at all, e.g. if there is the existing loss of ring continuity and then another connection has been broken a few sockets away during testing.
 
Voltage testers show continuity,

Voltage testers show voltage, Continuity testers show continuity. Horses for courses.

It's possible for a voltage tester or multimeter with high impedance input to display a normal-looking voltage with hundreds of kilohms of resistance in the circuit, off the scale of a continuity tester by a factor of 1000. Therefore in this situation testing voltage is probably misleading.
 

Reply to Live Earth Reverse in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi. I'm in the process of getting my qualifications and am taking on some small jobs for family to try and get some experience in. Today I was...
Replies
17
Views
858
I've just picked one of these up on a famous auction site. The voltages, low and high resistance ranges all appear to be working fine but it's not...
Replies
7
Views
295
I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
706
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
297
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
829

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock