tomspark93

-
Esteemed
Reaction score
339
I've been asked to install some 24v red/green traffic lights for some loading bays. Basically when the shutter doors go up the lights need to turn red and then when they go down they need to turn back to green to signal the lorry driver it's safe to pull away from the dock.

Has anybody installed these before and know the best way to do them?

I've attached my idea and would like to know if this would be a suitable solution? If it is then what kind of relay would I need as I'm not really familiar with them?

Cheers,

Tom

IMG_3157.JPG
 
You need to think about how this signalling system could fail and arrange your door contacts and relay contacts wired logic so that it fails leaving a safe indication to the driver of a Red light meaning 'Stop' or no Green light meaning not 'Safe to Move off'.

So, possible failures are:

1. the shutter door contacts.
2. the relay.
3. the relay contacts.
3. the power supply.
4. the fusing (non shown yet).
5. wiring damage.
6. lamp failure.
 
Also it may be a good idea to have some sort of timer in there, so the door needs to be closed a couple of seconds before green, goes instantly red when it opens.

If the limit fails the red lamp needs to come on.
 
What are you intending on using to sense the roller door is closed, a magnetic reed switch as used on security alarm systems?
 
Maybe they should think of the person inside closing the door presses a button when all is good to make the light go green and so on rather than rely on an automated process?
 
Thanks for the replies so far, a lot of Interesting points!
Maybe they should think of the person inside closing the door presses a button when all is good to make the light go green and so on rather than rely on an automated process?

Already suggested a switch so in one position the lights are red and the other position they are green but they want a "fool proof" system so that they don't just get left on.

What are you intending on using to sense the roller door is closed, a magnetic reed switch as used on security alarm systems?
Yes I was thinking about using a heavy duty shutter door contact
 
As opposed to fabricating your own system just contact companies which produce these lights who can provide controls which integrate with the shutter controls. This would ensure any safety requirements are complied with.
 
As opposed to fabricating your own system just contact companies which produce these lights who can provide controls which integrate with the shutter controls. This would ensure any safety requirements are complied with.
That's one of the questions I meant to get across in the op as I'd much prefer that for piece of mind/ease of install/quoting. I was wondering if anyone could recommend something?
 
I have never installed these but several companies supply them with the necessary control systems.
 

Reply to Loading bay traffic light in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I am trying to understand how a relay system works and have designed a circuit and a ladder diagram all as attached for an 8 PIN relay, a current...
Replies
14
Views
463
Hello all, I have a tail light for a '12 Ducati Panigale 1199 S, that I can't get working properly. The brake light / daytime running lights...
Replies
1
Views
593
I have a bathroom fan with a moisture detector that turns it on and off. It also has a control circuit to turn it on/off when moisture is not...
Replies
1
Views
285
I've fitted some led lights with power supply and mi light controller, they were working fine and all colours could be seen, then for some reason...
Replies
3
Views
682
Hi, I've just had some electrical work completed in the bathroom; I've recently refurbished the bathroom, replacing the old electric shower with...
Replies
39
Views
8K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock