Hi,
Looking to purchase a Trumpf laser table that uses 90 amps and wanting to run from a 150KW diesel generator. Can this be done and if so, what would be required for a UPS? Thank you
 
Your post is a liitle confusing do you have anymore information on the laser table and generator also how does the UPS fit into the setup
 
Hi, Sorry. The table specs are as follows:

Trumph TruLaser 3040
Watts 4,000
Type L32
Manufactured March 2012
Electrical Supply 460 V / 60 Hz
Full load current 90 Amps
Amp rating of largest motor 7.9 amps
Necessary fuse protection 3 x 160 Amp
Air supply 100 - 145 psi
Nitrogen supply 390 psi
Oxygen supply 210 psi


Have a 3 phase diesel generator that produces 150 KVA, 125KW

Looking to have the unit set up remotely where 3 phase power is not available.

Any help would be greatly appreciated. Thank you
 
You might want to check with Trumph if there is any special shut-down procedure / power requierments to allow key components to be cooled as the system stops.

That might point to a risk of damage if the generator cuts out in an unplanned manner, so then you may well be looking at a battery (or flywheel?) UPS as well to allow a few minutes graceful shutdown.
 

Reply to Looking to purchase a Trumpf laser table in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hi, can anyone recommend a good Green Cross Laser level, I have been looking a Milwaukee’s offering So, any feedback on that would be great...
Replies
14
Views
978
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
841
Hello Everyone -- So, I am looking to buy a used 5HP 3PH 208 V 10 inch Table saw --- (Motor Plate Data in Image) I am a DIY'er and in...
Replies
2
Views
535
Hi, The shower pull chord switch has snapped at my mom’s home and having unscrewed the switch I discovered a horror show(see pic). So I’ve had...
Replies
39
Views
3K
I am interested in having a home generator that would provide power to my home when the power is out during hurricane season, etc. I have 2...
Replies
0
Views
283

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock