Discuss Looped supply through garage? Look ok? in the UK Electrical Forum area at ElectriciansForums.net

chriso

DIY
Reaction score
2
Hi

Just bought this 1960s house, will be doing full rewire. Incoming supply splits and goes through hole in garage to next door. This is a looped supply?

From what I've read this can restrict us getting an electric car charger in future, that I can speak to the dno about unlooping.

Electrician said the earth cable clamp (coming from next door), clamping on to the mains at the bottom, was loose. Is that a dno issue?

How safe is this setup, sharing next door via a hole in the wall? I believe they are on old style fuses like this with no rcds. If anything were to blow or fire on their old electrics, would it quickly spread through here?

I don't want to annoy the neighbours by having the driveway dug up, but I also want to be safe.

On the full rewire, does this old bit of backboard have to stay? Or is it fine?

Thanks


elecbox.jpg
 
Doesn't look looped to me - tell-tale is 2 cables coming out the bottom of the cutout, you only have 1 and the cables out the top are just LN for your install
 
Thanks. So it's not a looped connection?

"What happens if you share an electricity supply with another property? When two properties share a single electricity service cabled, this is a ‘looped service’. These are often found in terraced or semi-detached houses. The service will enter into a property via premises 1 and be looped into premises 2. Everything else is the same as an overhead or underground connection."
Either way, if it is a single feed coming into our garage, going to both properties, what are the risks? What load can be put through here? What if we want a car charger? What if the neighbour circuits blow due to having 1960s circuits that haven't been updated?
 
Shared supply will be treated same as looped from dno perspective.
If looking for an ev charger in the future they will unloop for free, which could involve major groundworks, but at least you aint paying for it!
If you know the rating of the fuse then via 2 ct clamps you can still monitor the loads and group them via the zappi group monitor function

Have you actually cheked your neighbours to see if they have a meter? have seen cases and images online before of people having an unmetered supply... werent very happy when neighbours got it disconnected!

Should also say that if the dno become aware of this they may decide to enforce the remedial works... Had a situation in Bath where by one neighbour wanted an ev charger but was looped and fed next door. the neighbour wouldnt give permission and kicked up right fuss. was fuming when his power was off for a few hours as in the end they did all the remedial on my customers side and left the awkward one with a 60a supply and the old cables but my customer got a nice 100A supply with PME, my customer agreed to old cutout remaining in place but unused alongside a new one.
Long story short your neighbour doesnt have much say in the matter! dno can force the remedial work on them if they want, they have quite wide ranging powers.
 
Its a shared supply off the same cutout fuse, eg if the supply is fused at 100A, then that 100A is shared between the 2 property's. The other property will have a cutout fuse (maybe 60A) metering equipment etc.
My advice would be to speak to your DNO regarding EV charging in the pipe line, could be a cost involved to split the shared service? they will advice or maybe free of charge.
 
Last edited:
Hi

Just bought this 1960s house, will be doing full rewire. Incoming supply splits and goes through hole in garage to next door. This is a looped supply?

From what I've read this can restrict us getting an electric car charger in future, that I can speak to the dno about unlooping.

Electrician said the earth cable clamp (coming from next door), clamping on to the mains at the bottom, was loose. Is that a dno issue?

How safe is this setup, sharing next door via a hole in the wall? I believe they are on old style fuses like this with no rcds. If anything were to blow or fire on their old electrics, would it quickly spread through here?

I don't want to annoy the neighbours by having the driveway dug up, but I also want to be safe.

On the full rewire, does this old bit of backboard have to stay? Or is it fine?

Thanks


View attachment 105084
Yes, with them tagged off the outgoing side of your cutout fuse you probably want ukpn out to sort if your wanting a car charger etc, and yes their earth on that clamp doesnt look amazing either
 
Update.
Nice chap from National Grid came out and looked. Said that they can unloop it and give next door their own supply, but would have to dig up their drive and road.

The fuse (in behind the metal tie on the main incoming black box) was only rated 60amps. Is that fuse just for my property or covering both properties?

Eletrician with us said thats not enough for todays loads, especially for a 4 bed house and suggested it should be 80amps. National Grid guy said he's not sure if thats a chargeable service, because technically it's not a fault.

What would you do here? Anyone have any experience in how much they charge?

It seems bonkers that they can unloop a supply digging up the roads for free, but to change an inadequate fuse for todays needs is chargeable.

We don't have an electric car or heat pump, but will have elec fireplace, hob, oven, immersion heater, garden office etc.

Even if we unloop and next door get a nice new supply, presumably with a higher rated fuse, would we even get a fuse upgrade on our side?

He also said they wouldn't put fireproof foam in the hole between properties, they don't touch that and its down to residents.

Thanks
 


My neighbour needs Thiers unlooping for an EV charger. Normally they would go and do the work via 15 but are unable to access the property as the owner is recently deceased so they're going to joint from our driveway and tap into the main trunk there.

The image shows the local LV main and supplies to each house, not something I've seen before so thought I'd share
 
The fuse (in behind the metal tie on the main incoming black box) was only rated 60amps. Is that fuse just for my property or covering both properties?

Eletrician with us said thats not enough for todays loads, especially for a 4 bed house and suggested it should be 80amps. National Grid guy said he's not sure if thats a chargeable service, because technically it's not a fault.

From your image, it seems as though one fuse covers both properties.

Clearly this isn't ideal, but equally it mustn't have caused issues to date. The only people who can advise on the issue of cost is the network operator as they'll decide how much (if anything) works will cost.

I can't imagine this being chargeable, but would put forward the case that your neighbour could be left without electricity, should they manage to blow the main fuse while you were away on holiday - an unlikely circumstance, but one that would be difficult to argue against.
 
Never seen anything like this before, although from whats been said seems common?

Doesn't seem right, that your neighbours supply is in your property. Neighbours supply, and not DNO's cable. Seems a bit of a DNO bodge to me?
 
Hi

Just bought this 1960s house, will be doing full rewire. Incoming supply splits and goes through hole in garage to next door. This is a looped supply?

From what I've read this can restrict us getting an electric car charger in future, that I can speak to the dno about unlooping.

Electrician said the earth cable clamp (coming from next door), clamping on to the mains at the bottom, was loose. Is that a dno issue?

How safe is this setup, sharing next door via a hole in the wall? I believe they are on old style fuses like this with no rcds. If anything were to blow or fire on their old electrics, would it quickly spread through here?

I don't want to annoy the neighbours by having the driveway dug up, but I also want to be safe.

On the full rewire, does this old bit of backboard have to stay? Or is it fine?

Thanks


View attachment 105084
The ceiling does look like asbestos. If the property has an internal garage, there is a good chance it will be asbestos. It’s there as a fire break to stop the fire spreading to the rest of the property If it has a door into the property from the garage that could be asbestos as well Get it checked before you start work.
 
Last edited by a moderator:
Hi

Just bought this 1960s house, will be doing full rewire. Incoming supply splits and goes through hole in garage to next door. This is a looped supply?

From what I've read this can restrict us getting an electric car charger in future, that I can speak to the dno about unlooping.

Electrician said the earth cable clamp (coming from next door), clamping on to the mains at the bottom, was loose. Is that a dno issue?

How safe is this setup, sharing next door via a hole in the wall? I believe they are on old style fuses like this with no rcds. If anything were to blow or fire on their old electrics, would it quickly spread through here?

I don't want to annoy the neighbours by having the driveway dug up, but I also want to be safe.

On the full rewire, does this old bit of backboard have to stay? Or is it fine?

Thanks


View attachment 105084
Hi Chriso did you manage to find a solution? We are in a similar situation with our property that was splits into 2 different properties some time ago. We brought UKPN to request to unloop the service but they say that it is not a looped service but rather a single phase supply which laterally feeds my upstairs neighbour via a private cable...
 
Interesting that this should come up because I've got WPD (ok national grid) coming on Friday to look at a similar situation at a job I'm in the early stages of. In this case 2 supplies coming from 1 fairly new cutout. Tbh I don't think I've ever seen this before in my area and the guy at NG seemed quite surprised and said it wasn't 'correct'. I'm interested in what you all think about their likely reaction as the job will probably entail moving one of the supplies and it will be many brownie points for me if I can steer it in the 'no charge' direction.
Ignore the awful swa connection straight off the meter ....its coming out!!
 

Attachments

  • IMG_20230127_153750_240(1).jpg
    443.8 KB · Views: 25
Last edited:

Reply to Looped supply through garage? Look ok? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
927
Hello. Just a lowly homeowner here who is beginning to panic after a major house renovation regarding relocation of the main supply cable to the...
Replies
3
Views
2K
Hi, Can anyone tell me what material the main supply cable is wrapped with (I believe this cable is owned by the DNO). My concern is whether it...
Replies
21
Views
6K
I've had an EICR done on a property via a letting company I use, (they didn't inform us this was taking place), next thing an invoice comes...
Replies
11
Views
2K
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock