Hi
I’m still learning so forgive my stupid question. I’ve been testing a ring main off 4mm/1.5mm singles in metal trunking and conduit. My reading are:
L-L 0.91
N-N 0.90
E-E 0.80

I was expecting my R2 value to be 2.66 x 0.91=2.42

I this purely parallel path related??

many thanks
 
if each socket outlet etc is metal clad then in each socket the CPC is connected to the conduit via the front screws, this is in parallel to the cpc to the next socket etc.
 
Thanks for the replies guys. Problem is that the singles go into dado trunking drops and no metal clad sockets in the ring. Some have metal conduits bent into the plastic vertical drops and some have metal kopex but none are made of into plastic obviously. Which made me question the R2 value more as if it was parallel earth paths I’d understand the low reading
 
Also remember you only need a few of sockets to have near-zero ohms from the metallic surround to bring the E-E value down. You don't need all to be connecting.

And yes, that does make interpreting the E-E resistance difficult or even pointless. But at least your L-L and N-N and close enough for comfort!
 
If you are saying there is pvc trunking separating the steel trunking and the sockets, and all the sockets are plastic backed, I'd be inclined to do a continuity test between each end of cpc and the steel trunking.
Making assumption this is EICR not EIC is there a possibility someone has 'bonded' the steel trunking using the circuits cpc, or joined the bonding conductor to the cpc at least twice?
 
In a normal RFC (insulated surround) the E-E continuity gives you very high confidence all sockets have CPC continuity. Not absolute, as the CPCs could be twisted and have fallen out of one socket's E terminal, but still good confidence.

In the typical industrial situation (all metal trunking/conduit) you often don't need the CPC as the metalwork is doing the job and, short of major corrosion or stupid plastic-replacement work, is also a very reliable CPC.

But if you have the CPC used for multiple bonds and a mix of plastic socket supports there is really no guarantee that a low E-E reading is verifying (more or less) all sockets' CPCs. The good readings on L-L and N-N suggest things are probably OK, but if concerned you might want to do the figure-of-eight test and check a decent portion of the sockets have good low L-E results on that.
 

Reply to Low End to End R2 value Help in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
Hi Can anyone clear up or explain in a bit more detail what could potentially be causing the results I have. I have just tested a 32a ring main...
Replies
7
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
After fixing a few CPC related issues on a ring final I got the following results L-L = 0.47 N-N = 0.47 CPC-CPC = 0.69 R1+R2 Tested at 0.31...
Replies
3
Views
1K
Domestic house, ring final circuit on an rcbo, end to end tests: r1 = 0.95 ohms, rn = 0.98 ohms, r2 = 1.02 ohms. It's rare a reading is too...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock