Discuss low IR in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
22
hi did a IR on a shed board L-N was 0.11Mohms so took out the radial circiut and light circuit did them separately and was fine 299Mohms so why low when they are connected to the shed board????? dont do much testing so help be nice cheers
 
IR tests should be carried out with L and N dissed from the board, so that low reading is irrelevant.
 
IR tests should be carried out with L and N dissed from the board, so that low reading is irrelevant.
Hi Tel don't normally question your replies, but looking at table 10.3.3 in the OSG it says.
"For an installation operating at 400/230V , although the IR value of 1Mohm complies with BS7671, where the IR reading is less than 2Mohm the possibility of a latent defect exists. in these circumstances each circuit should be tested separately" The original test was obviously a global test at the board.
 
hi did a IR on a shed board L-N was 0.11Mohms so took out the radial circiut and light circuit did them separately and was fine 299Mohms so why low when they are connected to the shed board????? dont do much testing so help be nice cheers

Why were you testing the shed?
 
Surely you must have seen a difference at some point!

Does the shed have a cu and if so what type? What is at the house end of the circuit? How many circuits in the shed?
 
I take it the board has a rcd main switch it could be reading across that. Switch off the MCBs and take the supply neutral from the neutral bar.
 

Reply to low IR in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
664
So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
404
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
619
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
653
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock