Discuss low IR in the UK Electrical Forum area at ElectriciansForums.net

Just the way I do it - thoroughly.

In this case it would have saved time and I'm personally not keen on the linked live to neutral test either
 
Where practicable I always test the entire dis. board in parallel. As stated RCBOs can make that impracticable.

But either way we need to consider the effect of the results in parallel, as the minimum values of insulation resistance quoted in BS 7671:2008 (2015) are for the whole installation, or in larger installations a distribution board with all final circuits connected in parallel. They are not minimum values for a single final circuit.
 
It would not have been the end of the world,to test at the neutral bar/MCB's,while the circuits were disconnected,and work out where this reading originated from,including any issue with the actual board.

I could not have left,before answering my own question ;)
 

Reply to low IR in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
652
So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
403
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
612
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
646
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock