Possibly a daft one this lads but any insight welcome. Have set a dummy rig up at home and am trying to replicate a low resistance fault on a ring main. No prob getting off scale high and zero readings but anyone think of a way of creating a low but not zero reading.
 
Since it need to be resistance is there any possibility of circuit being energised
(Resistor will become an electric Fire -or- lightbulb ..(practical examples rather than) some fire risk !
Do you want poor IR type values ?
 
You could run a 100m reel of 1mm down the garden.
Join brown and blue at the far end.

200m of 1mm should have a resistance that is low but measurable.
Keep the current below 13A and not for long durations and all should be fine.
 
Depends what you call a low resistance, but as mentioned, a 230V lamp - e.g. halogen lamp (tens of Ohms, depending on rating), or a 230V neon (fraction of a MOhm).

Plus you don't say if this is between L & N, or between two different conductors such as a N to E low resistance?
 
A man after my own heart! Delete Facebook,and get experimenting in the garage ;)

I will describe a method of inserting a fault test-bed,in to your rig,which i made many years back. All you need is a piece of board or plastic,1/2" thick,12" x 4" with two,fixed 3 terminal connectors or chocky blocks,one at each end.
This is inserted anywhere you like,in a ring or radial circuit,on your board.

Inbetween these two connectors,is your play area. I had several standard layouts,and will describe a couple.

One,was a 12" piece of T&E,with the middle 4",carefully stripped of sheathing and insulation,to reveal three,bare,conductors. These can have any number of materials laid across,or placed under,2 or 3 of them,and tested accordingly.

Damp or wet cavity insulation,plasterboard and brick,being favourites,but i never ran out of ideas....a handful of ashes,from any common building material,then dampen it....i even remember using dead mice...dry or fresh:oops: ...basically,it is an operation of deliberately using mediums you will encounter in real life,and practising with your test device,so the readings correlate to what you know,rather than what you are seeking,which invariably will be the case in the field.

The main thing you are aiming for,is NOT to be surprised,when testing on an actual installation,and getting confident,with your chosen test instruments.

There is no wrong material to introduce in to a circuit....nature and the great British public,will see to that...you can take that, from a man who,at the age of fifteen,woke one morning,desperate to see what the resistance was,of a single strand of galvanised,barbed wire,around a 4 acre field :cool:
 
Low resistance high power resistors can be bought from RS, etc. Or Ebay if you want a better price! Obviously make sure the max working voltage is high enough.
 
A man after my own heart! Delete Facebook,and get experimenting in the garage ;)

I will describe a method of inserting a fault test-bed,in to your rig,which i made many years back. All you need is a piece of board or plastic,1/2" thick,12" x 4" with two,fixed 3 terminal connectors or chocky blocks,one at each end.
This is inserted anywhere you like,in a ring or radial circuit,on your board.

Inbetween these two connectors,is your play area. I had several standard layouts,and will describe a couple.

One,was a 12" piece of T&E,with the middle 4",carefully stripped of sheathing and insulation,to reveal three,bare,conductors. These can have any number of materials laid across,or placed under,2 or 3 of them,and tested accordingly.

Damp or wet cavity insulation,plasterboard and brick,being favourites,but i never ran out of ideas....a handful of ashes,from any common building material,then dampen it....i even remember using dead mice...dry or fresh:oops: ...basically,it is an operation of deliberately using mediums you will encounter in real life,and practising with your test device,so the readings correlate to what you know,rather than what you are seeking,which invariably will be the case in the field.

The main thing you are aiming for,is NOT to be surprised,when testing on an actual installation,and getting confident,with your chosen test instruments.

There is no wrong material to introduce in to a circuit....nature and the great British public,will see to that...you can take that, from a man who,at the age of fifteen,woke one morning,desperate to see what the resistance was,of a single strand of galvanised,barbed wire,around a 4 acre field :cool:
What a cracking reply that is. And much appreciated. Will be on the rig first thing tomorrow having a go at that. Can't see me getting any sleep tonight. Thanks again. Will get back to you with the readings.
 
I have 12 inches of green coated thin steel garden wire with (Coaxed-copper-wrapped-"soldered ends") .. for about 0.07 Ohms Hard wearing "standard"!

Hi,i can not remember exactly what the barbed wire reading was,,,maybe 10 Ohms,i do remember it being less than calculated,but the Buzzcocks were playing,and that Mk8 had no calibration,so.....;)
 

Reply to Low resistance fault replicated on a made up rig in the Lighting Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Slightly strange one this, replaced a few socket fronts in a dining room today, all wiring original but new plasterboard on a studded wall. Its a...
Replies
4
Views
1K
Hello all, First of all I apologise if this is in the wrong forum, I figured the general forum may be the best bet :) Thank you for taking...
Replies
3
Views
539
I'm new to this but stuck with an issue, so I'm looking for some help wherever possible. I have just completed a rewire, which I have a potential...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock