Discuss Main Bonding plastic pipes in the Electricians' Talk area at ElectriciansForums.net

Reaction score
17
Hi again,

a kitchen has been ripped out, the main water stop was in there. it was all lead and copper water pipes and a main bond was to be run. However matey has lopped these pipes off and left about 4 inches of lead pipe coming in and then gone and replaced with plastic pipes. so would the small length of remaing lead pipe need bonding?
 
Hi again,

a kitchen has been ripped out, the main water stop was in there. it was all lead and copper water pipes and a main bond was to be run. However matey has lopped these pipes off and left about 4 inches of lead pipe coming in and then gone and replaced with plastic pipes. so would the small length of remaing lead pipe need bonding?


It will indeed need bonding to the MET i'm afraid, as it's still introducing an extraneous earth into the property!!
 
Without seeing the area and taking into account other factors that may have a bearing on my decision I have to go with whats in the BGB and GN 8:
411.3.1.1 & .2 ..... SHALL connect to the M.E.T extraneous-conductive-parts including...(i) water installation pipes.
GN8 ...... ALL e-c-p to be bonded to the MET.
 
this is a picture, i know theres a clamp on there, but its cream crackered and fairly seized up... and does it matter if the bond is before or after the stop cock, i know the continuity is there between the cock, but normally?.....i dont like typing cock so much either
 

Attachments

  • IMG_2059.jpg
    291.7 KB · Views: 135
especially since i=p/u has moved to scotland. LOL. :waving:
 
this is a picture, i know theres a clamp on there, but its cream crackered and fairly seized up... and does it matter if the bond is before or after the stop cock, i know the continuity is there between the cock, but normally?.....i dont like typing cock so much either

Plumber dropped one there.

That short bit of copper after the old siezed-up stop cock is the ideal place to fit a new one and then continue in plastic.

Must have been done by a spark who "knows a bit" about plumbing !!
 
I quite agree, although I'd have preferred to see another inch or two of copper.

Well you can have that if you want.

The plastic straight coupler is demountable and reusable - it just unscrews - and the short bit of copper is connected to the stop cock with a compression fitting, so you only need a longer bit of 15mm copper and a new 15mm olive to reconnect to the stop cock, then shorten the plastic pipe - remember to refit the insert into it - and shove the coupler back onto it.

Personally, I would have prefered to have the whole thing in copper with not a bit of plastic anywhere on the job, but I'm old fashioned.
 
Well they seemed to be having a bit of bother with lunatics running around with guns and shooting people through the knee caps at the time and I'm rather fond of mine.

Is that all :)
 
hmm, i meant that the old bonding clamp is seized, I didn't try for long but the screw started to snap so i can't reuse that clamp, and as far as I'm aware the stop cock is old but functional still....

So that short bit of copper after the stop cock still needs a main bond?
I think the rest of the pipe before the stopcock is wrapped in something, im not sure. it was all a mess when i arrived as there was a gas leak with a drop of 8.5 milibar per whatever unit is used and the ceiling had been pulled down, revealing a second ceiling which was pulled down and not tidied very much at all
 
hmm, i meant that the old bonding clamp is seized, I didn't try for long but the screw started to snap so i can't reuse that clamp, and as far as I'm aware the stop cock is old but functional still....

So that short bit of copper after the stop cock still needs a main bond?
I think the rest of the pipe before the stopcock is wrapped in something, im not sure. it was all a mess when i arrived as there was a gas leak with a drop of 8.5 milibar per whatever unit is used and the ceiling had been pulled down, revealing a second ceiling which was pulled down and not tidied very much at all


OK .. sorry I thought you meant the stop cock was seized.

As for the gas leak .. that cannot be ignored!!
 

Reply to Main Bonding plastic pipes in the Electricians' Talk area at ElectriciansForums.net

Similar Threads

Not sure on this one. Mains water is coming up from the ground in lead pipe in bathroom. 2 inches of copper pipe before the stop tap. All...
Replies
4
Views
1K
Hello, Carrying out remedial work on a commercial site and I've come across a metal out building that has a water supply to it. The water pipe...
Replies
6
Views
1K
Disclaimer: I'm not going to attempt this job myself, I want a professional to do this job properly since I consider it non-trivial and need it...
Replies
2
Views
954
Did a eicr on a upstairs flat, there is 1 main bonding cable from the consumer unit, the gas pipe comes from the gas meter outside and up the wall...
Replies
21
Views
3K
Hi, Small flat, currently has a small'ish feed water tank, top of a cupboard, feed through a wall into under stairs cupboard. Hot water tank...
Replies
5
Views
464

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock