I'm not quite sure I'm following all of this myself.

If the tails are 120mm and it is TN-C-S then Table 54.8 gives 35mm for the main bonds - that seems fine. Are the service pipes bonded from the incomer, or from the various DB at the ends of the sub-mains?

However, assuming the SWA is 4-core than it would be met a 95mm from the linked table on the basis of adiabatic equivalence. However, for PME fault currents of a long duration I was imagining you would look at the approximation of steel being around 8 times copper for the same CCC and that is where @westward10 is getting the 240mm SWA from (e.g. Prysmian table has 4-core 240mm SWA having 289mm of steel so about 36mm copper equivalent).

Outside of the PME fault case, the issue for the SWA armour would be more end of circuit Zs and the adiabatic for the OCPD at the source (assuming it is not directly off 120mm tails - please tell me they have not been that stupid?)

So definitely main bonds need upgraded to 35mm.

Not so obvious is if the SWA is OK and that would depend on meeting sub-main Zs for disconnection times and the adiabatic (we would like to think this was done originally, even if the TN-C-S requirements are more recent) AND if they are also bonded to extraneous parts.

If 'also' then would the SWA armour only need to meet the 16mm of Table 54.8? If so it is still looking at 120mm so not met on existing cables and then it would be down to the real nature of bonding at sub-boards and then to decide if added CPC can be run in. TT'ing them is always a possible idea, but not likely to be a better idea!
 
@pc1966 thanks for your post.
My understanding is that the OP has 120mm tails at the incomer, then SWA of various sizes from 25 to 50 feeding sub mains in other buildings.
I think we all agree the main bonding needs to be upped to 35 sq mm in the building the incomer is in.

If 'also' then would the SWA armour only need to meet the 16mm of Table 54.8?
That is basically my question too, expressed another way. I have never been content that I had full understanding on this point.

If there is a situation where there are no parallel paths between the incomer building and the remote buildings via services (no linked extraneous conductive parts such as a common metal water pipe) does the csa of the bonding at the remote building need to meet the onerous bonding requirements of the origin?
One could argue that table 54.8's value can't vary within an installation as it references the supplies PEN conductor.
But equally if the only things being bonded are localised services, then having a bonding conductor bigger than the line conductor seems over-zealous, and this might be one for a departure and a risk assessment.

Conversely if there were proven parallel paths then having the same size bonding at the remote building feels necessary as the source of the fault current could be subject to a considerably higher OCPD or even the suppliers fuse in the main building. This appears to be the one-size-fits-all position that the regs take.

However, assuming the SWA is 4-core than it would be met a 95mm from the linked table on the basis of adiabatic equivalence.
I follow that logic and agree - I arrived at 95 sq mm too from a purely CPC perspective.
However, for PME fault currents of a long duration I was imagining you would look at the approximation of steel being around 8 times copper for the same CCC and that is where @westward10 is getting the 240mm SWA from (e.g. Prysmian table has 4-core 240mm SWA having 289mm of steel so about 36mm copper equivalent).
This is where I get a little lost.
Is it right to use k1/k2 with k1 as 46 and k2 as 143 from tables 43.1 and 54.4 respectively; this gives the answer as 92.9 sq mm.
The linked table shows 4 core 240 SWA having 289mm of steel (agreed) and 92.9 sq mm copper equivalent as it uses the same calculation.
Or are there better reasons to adopt the multiple by 8 method, something I've read many times on forums but never to my knowledge seen in the regs.
 
@pc1966 thanks for your post.
My understanding is that the OP has 120mm tails at the incomer, then SWA of various sizes from 25 to 50 feeding sub mains in other buildings.
Just noticed the OP's comments later on about other buildings. That gets trickier as not so easy to guarentee services are the same (i.e. one water pipe for all site, etc) and structures are obviously not the same!
I think we all agree the main bonding needs to be upped to 35 sq mm in the building the incomer is in.
Yes, agreed.
That is basically my question too, expressed another way. I have never been content that I had full understanding on this point.

If there is a situation where there are no parallel paths between the incomer building and the remote buildings via services (no linked extraneous conductive parts such as a common metal water pipe) does the csa of the bonding at the remote building need to meet the onerous bonding requirements of the origin?
One could argue that table 54.8's value can't vary within an installation as it references the supplies PEN conductor.
But equally if the only things being bonded are localised services, then having a bonding conductor bigger than the line conductor seems over-zealous, and this might be one for a departure and a risk assessment.
The thing about Table 54.8 is the assumption that under open-PEN faults the max bond currents depend on the supply cable size.

Now clearly there is some dependence but not as obvious as the usual fault-clearing adiabatic that is down to OCPD and clearance time. In the open-PEN case you could have 1A fuses in the DNO cut-out and it might make little or no difference!

How big the earth fault current would depend on the point the PEN opened (specifically the unbalance between phase loads down-stream of the fault), the DNO cable impedance (so cable size is a factor here) and the impedance from extraneous parts back to the origin (transformer neutral).

I guess that 58.8's argument is along the lines of "bond big enough only to roast if the DNO cable is roasted" with maybe the guide that under most cases (effective site Ra of the order of a few ohms or higher) you won't see the max possible unbalance current as when the neutral goes floppy the load currents will adjust to reduce it (and light-loaded phase blow electronics...) and the Ra will dominate the answer.

I suppose you might argue that the site load itself is the closest an open-PEN fault could be, and then it is down to a similar bond size to whatever reduced-size neutral that would be acceptable for a supply cable. If you have a big load that could be the case, but you might have more fault current that your own site if there is a lot of unbalance on the supply from multiple sites. Presumably the folks who drew up 54.8 have knowledge of the sorts of imbalances the DNOs might see along segments of their network to come to those sort of figures. Which is where the sub-main and remote building bonding issue get tricky...

I follow that logic and agree - I arrived at 95 sq mm too from a purely CPC perspective.

This is where I get a little lost.
Is it right to use k1/k2 with k1 as 46 and k2 as 143 from tables 43.1 and 54.4 respectively; this gives the answer as 92.9 sq mm.
The linked table shows 4 core 240 SWA having 289mm of steel (agreed) and 92.9 sq mm copper equivalent as it uses the same calculation.
Or are there better reasons to adopt the multiple by 8 method, something I've read many times on forums but never to my knowledge seen in the regs.
The thing with the adiabatic equivalence is it takes in to account both the higher resistivity of steel AND the greater thermal capacity of the bigger conductor that it points to.

So the approx factor of 8 for conductance leads to similar R and so similar I^2R losses under current flow, i.e. same sort of heat per unit length. But under the short-duration fault case when you make the adiabatic assumption that heat is not going in/out of the system, what gives to the change in temperature is both the energy input (i.e. I2t*R) and the thermal capacity (which greater mass of material from lower conductance for a given R increases). Hence the factor of about 3 instead of 8 (so your resistance might still be almost 3 times that of the copper equivalent but you now have almost 3 times the steel material to soak up the heat pulse).

But the open-PEN case is not short-lived. You could be running the PEN current via the bond for potentially hours or even days before it is fixed, and supply OCPD or switching of the site isolator could make no difference (unless you are breaking regs generally-speaking by opening the CPC) depending on the fault location, etc. In that case the thermal capacity of the CPC/bond is irrelevant, it is now the dissipation (I^2R) and resulting ability of the cable to get rid of heat (i.e. "method") that sets the conductor temperature and resulting risk of insulation damage or even a fire.
 
Last edited:
I'm going to throw me tin hat in the ring GN8 page69 shows
fig 5.14 for out buildings ,considering it a TNCS and going to the out buildings so that now makes that a TT ,for both building
say a pen fault arises then both buildings would now be live
has PC states ,so to the outer building needs to be TT and not reliant on tother end @cliffed you're option is either RCD IT or make it TT.
@ tiny tim howard I'm on the same page has you.
 
I'm going to throw me tin hat in the ring GN8 page69 shows
fig 5.14 for out buildings ,considering it a TNCS and going to the out buildings so that now makes that a TT ,for both building
say a pen fault arises then both buildings would now be live
has PC states ,so to the outer building needs to be TT and not reliant on tother end @cliffed you're option is either RCD IT or make it TT.
@ tiny tim howard I'm on the same page has you.its A good option
It’s a good option but I doubt the Client will have it done.
They are 400v TPN DB’s, Swa into the DB,Rcd could be before main switch,T/D 100ma
The buildings are Steel fabrication some have extraneous conductive parts entering Water/Gas others just the structure.
MEBPC would be 35mm if Tncs
 
say a pen fault arises then both buildings would now be live
has PC states ,so to the outer building needs to be TT and not reliant on tother end @cliffed you're option is either RCD IT or make it TT.
The issue I wonder about is whether you can actually TT the outer building in this situation? If the outer building shares extraneous
metalwork with the main house (water pipe), then that metalwork will still become live even if the shed is TT. So to effectively TT the outer building would it not require capping the extraneous part entering the shed with plastic??
 

Reply to Main earth bonding protective conductors in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi there, Just a quick question. Does a main protective bonding conductor require UV protection when run outside? I am under the impression that...
Replies
3
Views
708
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
906
Hi all, just looking for guidance on how you would code a 2.5mm main earthing conductor on a property with 10mm line conductor. Basically on a...
Replies
2
Views
2K
Morning All, Think I'm having a brain fart but I have a 70mm2 4 core SWA with a separate 35mm2 CPC. Earthing is TNS with main bonding...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock