Discuss Main supply to fire alarm panel in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Ian1981

-
Mentor
Esteemed
Arms
Reaction score
3,818
what is everyone's opinion about fire alarm supply's to the main panel.
Im of the understanding that the mains is part of the integral fire alarm system, thus should be of a different colour for identification to the other building wiring normally red.
I have a colleague at work who disagrees and every chance he gets he's installed the mains in standard twin & earth or if needed LSOH cable.
Cheers.
 
what is everyone's opinion about fire alarm supply's to the main panel.
Im of the understanding that the mains is part of the integral fire alarm system, thus should be of a different colour for identification to the other building wiring normally red.
I have a colleague at work who disagrees and every chance he gets he's installed the mains in standard twin & earth or if needed LSOH cable.
Cheers.
The guy I use to design/commission makes us use red.
 
just found this bit of info that someone has quoted from BS5839

Recommendations for mains power supplies
The following recommendations are applicable to the low voltage mains supply to the system.

NOTE 1 This supply should be regarded as an integral part of the fire alarm system, particularly for the purpose of certification
of the system (see Clause 41), regardless of whether the electrical installation within the building is provided by the organization
responsible for installation of the fire alarm system.

"All fire alarm cables should be of a single, common colour that is not used for cables of general electrical services in the building, to enable these cables to be distinguished from those of other circuits."
NOTE 13 The colour red is preferred.
 
just found this bit of info that someone has quoted from BS5839

Recommendations for mains power supplies
The following recommendations are applicable to the low voltage mains supply to the system.

NOTE 1 This supply should be regarded as an integral part of the fire alarm system, particularly for the purpose of certification
of the system (see Clause 41), regardless of whether the electrical installation within the building is provided by the organization
responsible for installation of the fire alarm system.

"All fire alarm cables should be of a single, common colour that is not used for cables of general electrical services in the building, to enable these cables to be distinguished from those of other circuits."
NOTE 13 The colour red is preferred.
Yeah I've got a screenshot on my phone of this.
However is it final or just a recommendation?
 
Im with Lee. Our local council dictates the colour in our area, they have chosen red for fire alarm installations to separate the fire alarm from the normal building supplies. Strange that the council has a say but we have a massive contract with them so were not falling out over a cable colour:)
 
Red FP according to my fire alarm Designer, I have got 5839 in the office but I don't like anybody on here enough to drive there and look at it. :p
 
Red fp 200 or MI , should be fed from the main panel,not a sub board and I also believe it should not be 30ma rcd protected (not sure if thats a reg or just guidance).
 
Yeah I've got a screenshot on my phone of this.
However is it final or just a recommendation?
If I hav
Red fp 200 or MI , should be fed from the main panel,not a sub board and I also believe it should not be 30ma rcd protected (not sure if thats a reg or just guidance).
i think non rcd is preferred but if it has to be 30mA for additional protection purposes buried in a wall especially with metal construction then an rcbo isn't too bad as it's individually protected.
 
FP 200 gold or FP plus can be installed without additional protection.
Does the foil count as earthed metal protection then as would swa on armoured cable?
I'm aware bs 7671 gives examples of the types of British standard cables which can be used , I'll have a look tomorrow.
 
Last edited:
We could always ask @westward10 what it says in the Best practice guide.
 
This explains it better than I can

Fire alarm cables for use in thin walls or partitions - http://www.voltimum.co.uk/articles/fire-alarm-cables-use-thin-walls-or-partitions-0

Basically because it meets the nail penetration test the same as BS8436 cable but also BS8436 cable can only be installed without additional protection if buried in a wall<50mm etc if its on a type b breaker/RCBO

http://www.napitonline.com/downloads/CP 3 08 P 11-12 BS 8436 Cables.pdf
Nice advice lee.
That's why I come on the forum cheers
 
Supply to a fire alarm panel needs to be wired in Enhanced fire proof cable. T & E or basic FP200 is against the regs. Enhanced cables include Piro, Armored or FP200 Enhanced. Colour is not important unless requested in the specification, personally I would recommend white FP or black Armored, to identify the cable is being used for 230v, preventing confusion with red loop or zone cables. A double pole, lockable fused spur should also be used local to the control panel.
 
Supply to a fire alarm panel needs to be wired in Enhanced fire proof cable. T & E or basic FP200 is against the regs. Enhanced cables include Piro, Armored or FP200 Enhanced. Colour is not important unless requested in the specification, personally I would recommend white FP or black Armored, to identify the cable is being used for 230v, preventing confusion with red loop or zone cables. A double pole, lockable fused spur should also be used local to the control panel.
If supply to panel is installed in Enhanced fire proof cable , would it go down as a departure on the eic as this cable is not covered by bs 7671?
 

Reply to Main supply to fire alarm panel in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I am doing renovation to a cafe in Scotland at the moment and after speaking to the local council the building requires the minimum standard for a...
Replies
5
Views
1K
Hi I'm in need of some advice. First of all i'm not an electrician but do have an understanding of electrics as i come from an electronics...
Replies
4
Views
609
Hi guys been asked to put a radial in for spurs for a fire alarm panel supply is it okay to use red FP200 to carry 230v? If so or not could you...
Replies
11
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Been having issues with a pair of linked Actulux SVM controllers. If the fire alarm is triggered the controllers show 'Alarm' and the AOVs open...
Replies
2
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock