Discuss main switch question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Still no requirement for socket circuits to be provided with RCD protection.
Yes there are circumstances where it may be advisable, or the simplest solution to provide RCD protection for such a circuit.
However it still remains that there is no requirement in BS7671 for such circuits to be provided with RCD protection, except in some circumstances where the installation is considered to be a special location.
Doesn't matter whether there is a dwelling involved or not.

411.3.3

Addition Protection RCD

Socket outlets not exceeding 20 A
 
The difference is the regulations say socket outlet and not circuit. For example you could have the circuit installed surface so doesn't require RCD protection but you would install a RCD socket outlet to comply.
 
No, it came into effect on the 1st Jan 2015 but the 'old' regs don't cease until the 30th June 2015 so the 3rd amendment is actually Currently in effect.

It was published on 1st January, with an effective date of 1st July. So BS 7671:2008 (2013) is still current.
 
No, it came into effect on the 1st Jan 2015 but the 'old' regs don't cease until the 30th June 2015 so the 3rd amendment is actually Currently in effect.

Wrong! this is of the IET website;


Amendment No. 3 to BS 7671 Wiring Regulations will be published on 5 January 2015, and will come into effect on 1 July 2015. The new reference for the book will be ‘BS 7671:2008+A3:2015’.
All new installations must comply with BS 7671:2008+A3:2015 from 1 July 2015.
In this update, a number of potentially life-saving changes have been proposed, which include, but are not limited to, changes to:
consumer unit enclosures (to come into effect January 2016);
wiring in escape routes;
changes to earth fault loop impedances for all protective devices;
the risk assessment approach for the omission of RCDs in non-domestic situations;
updated EIC and EICR forms; and
changes to definitions throughout the Wiring Regulations.
 

Reply to main switch question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Can a domestic consumer unit feed another consumer unit, via the Main Switch. Details are: domestic property with 100A single phase supply...
Replies
9
Views
480
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
Hi there, Any advice on this would be greatly appreciated! (Note, this is not a DIY, I'm using a fully qualified electrician, just posting here...
Replies
8
Views
737
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
5
Views
2K
Deleted member 155212
D
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
762

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock