Discuss Mains wired smoke / heat / CO detector question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
3
Hi Guys

We're having work done to insert an open plan kitchen-diner and snug seating area plus wood burner into already existing extension. One load bearing wall is being knocked through.

Electrician just bumped his quote up by £820 to cover replacing this consumer unit and moving it up the wall (above where the fridge will be going), breakdown:

Consumer unit replacement (even though no new circuits) = £500

Plus he's said we need new mains wired:
2 x smoke detectors (top and bottom of stairs in main house, not even area we're having work done) @ £80 each = £160
1 x heat detector in new kitchen = £80
1 x carbon monoxide detector in new snug area = £80

House built in 1982 and has one battery operated smoke detector at bottom of stairs.

1. Are these mains powered devices necessary as we'd be more than happy with the long life 10 yr battery powered devices?

2. Is it necessary to replace and test etc. the original consumer unit (photo below)?

consumer unit.jpg
 
On the face of it there's no requirement to swap out a perfectly good distribution board. It may not be the very latest but is still fit for purpose and a very good make.

As for smokes/heat/Co detectors etc as I'm guessing yours is a private property then there's no requirement for mains powered devices although they are my preferred option.

Has the electrician mentioned membership of any scheme such as NICEIC/STROMA/NAPIT etc?

I would seek quotes from another two electricians, if you know anyone that could recommend one then great if not post up a rough location then I'm sure a forum member would be close by and able to quote for you.
 
On the face of it there's no requirement to swap out a perfectly good distribution board. It may not be the very latest but is still fit for purpose and a very good make.

As for smokes/heat/Co detectors etc as I'm guessing yours is a private property then there's no requirement for mains powered devices although they are my preferred option.

Has the electrician mentioned membership of any scheme such as NICEIC/STROMA/NAPIT etc?

I would seek quotes from another two electricians, if you know anyone that could recommend one then great if not post up a rough location then I'm sure a forum member would be close by and able to quote for you.

Thanks Strima, appreciate the reply. Electrician hasn't mentioned any schemes.

I'm in Selby area, North Yorkshire. As a new member to the forum I didn't really know how local to put my location so will update. Also, yes, private property, thanks.
 
open that cover of the consumer unit ,so we can see if it justifies that price ,was their any testing done .
That's the original consumer unit, installed prior to us purchasing the property.

love when the ops put location uk ,their has well put the moon ,where I'm on .;)
As a new member I didn't know how local to put my location, as a bit of sound advice you could have replied in a friendlier manner to say that providing a local location would allow for local quotes etc. Thanks.
 
House built in 1982 and has one battery operated smoke detector at bottom of stairs.

1. Are these mains powered devices necessary as we'd be more than happy with the long life 10 yr battery powered devices?
We're having work done to insert an open plan kitchen-diner and snug seating area plus wood burner into already existing extension
death by fire or sleep and you will not wake up, you choose .
 
You don’t have to have mains wired interlinked alarms, as already stated.

However, as you are having building work down, with building control involvement? Do they have any stipulations, I had to go for mains powered ones a few years back with my extension.
 
You don’t have to have mains wired interlinked alarms, as already stated.

However, as you are having building work down, with building control involvement? Do they have any stipulations, I had to go for mains powered ones a few years back with my extension.
Thanks Midwest

Yes, I should have said in the OP, building control will be involved, sorry about that. I've just called building control to check and they ummed and arred a bit before saying mains wired would not be required, didn't fill me with confidence to be honest.
 
Thanks everyone.

Just had a chat with electrician and explained what building control said about not needing mains powered sensors. He's said to check with main builder and the building inspector, so will do that.

He also says because the consumer unit is being moved it needs to adhere to updated regs, so we need a new "gen-18 unit" and "these are a bit more pricey than they used to be". - Can anyone confirm if this is the case?

Losing the will a bit here, phew.
 
Hmmm. How far is CU moving, and are any of the circuits being extended?
CU is moving about 6ft up the wall it's currently fixed to, mains cable runs up the same wall.

We've not anticipated any circuits being extended as the current rooms already have lights, sockets, oven etc. circuits in them. There will be some moving of wiring but doubt there'll be additional circuits needed. There are 3 spare module slots in the current CU if that makes any difference.
 
Thanks everyone.

Just had a chat with electrician and explained what building control said about not needing mains powered sensors. He's said to check with main builder and the building inspector, so will do that.

He also says because the consumer unit is being moved it needs to adhere to updated regs, so we need a new "gen-18 unit" and "these are a bit more pricey than they used to be". - Can anyone confirm if this is the case?

Losing the will a bit here, phew.
I'm glad you will sort it out ,I can now take the pop corn out of the oven .:D
 
CU is moving about 6ft up the wall it's currently fixed to, mains cable runs up the same wall.

We've not anticipated any circuits being extended as the current rooms already have lights, sockets, oven etc. circuits in them. There will be some moving of wiring but doubt there'll be additional circuits needed. There are 3 spare module slots in the current CU if that makes any difference.

IMO then is just moving an enclosure & I would suggest comes under maintenance, & does not warrant latest. In such a scenario, I would contact my Scheme for guidance, but as I'm no longer in a Scheme I can't.
 
no ,trying to help you ,if you having any work done then the only people to give you advise this your local building control .

Buzz - I know you're just messing mate but is there any chance you could answer the questions I've asked and genuinely give your expert view on this situation
Just had a chat with electrician and explained what building control said about not needing mains powered sensors. He's said to check with main builder and the building inspector
I put that in post #15 for you .
 
its about time the government need to put on tv about part p, so people like you ,would under stand how things work ,your building inspector and builder should advised you straight away .and the spark that doing the job .
 
you can get battery only detectors that interlink wi-fi. see screwfix.
https://www.NoLinkingToThis/p/fireangel-wst-630q-wireless-interlink-thermoptek-smoke-alarm/87048
 
He also says because the consumer unit is being moved it needs to adhere to updated regs, so we need a new "gen-18 unit" and "these are a bit more pricey than they used to be".

that is total Bollox. re-siting a perfectly good CU is compliant.

a "gen 18 unit " is just the same gubbins in a metal box.
 
If the CU is being moved 6ft up the wall, its not going to be at a regulation height, ie it'll be too near the ceiling. You'll need steps to reset a breaker.

Nothing wrong with using battery powered smokes with radiolink interconnect from Aico for example. More expensive to buy, but saving time on install. (4 detectors, 30 minutes tops) and theres no cables to run under floors etc. No damage to existing decoration.

The only thing not regulation with the board is that its plastic. Buy a metal one yourself and use the existing breakers. Just has to be the same make of board.

Is this electrician already doing work for you or is there a chance of getting other quotes?
 
regulation height for CUs ( along with dwarf accessible light switches) applies ony to new builds.
 
I put that in post #15 for you .

See post #11 mate. I'd already explained that I'd spoken to building control and they'd contradicted the electrician.

I can only go on what I'm told up-front so if I get an updated quote just before work starts with an unexpected extra £820 for the extra electrical work I'm well within my rights to question that. Good job I did too, eh, as if I didn't I wouldn't be here getting good advice from people who know a bit more than I do.

What I've worked out today is that there is a disconnect between electrician and the builder and inspector. I'll find out tomorrow morning exactly what the building inspector expectations are in terms of mains wired sensors.

Your comments throughout have added nothing of value but the guy trying to get the advice got it from those that would rather be helpful. Sorry if you've taken some kind of offence early on in this thread, I'm only asking questions mate....
 
A bit of banter can keep the mood of the forum nice and light. Don't worry about it. We generally manage a 25/75 split of useless/useful so not too bad :)
 
If the CU is being moved 6ft up the wall, its not going to be at a regulation height, ie it'll be too near the ceiling. You'll need steps to reset a breaker.

Nothing wrong with using battery powered smokes with radiolink interconnect from Aico for example. More expensive to buy, but saving time on install. (4 detectors, 30 minutes tops) and theres no cables to run under floors etc. No damage to existing decoration.

The only thing not regulation with the board is that its plastic. Buy a metal one yourself and use the existing breakers. Just has to be the same make of board.

Is this electrician already doing work for you or is there a chance of getting other quotes?
Thanks littlespark

The main builder has got his preferred electrician, I've just spoken to him (builder) and explained I'm not happy with the extra £820 and want him to check with building inspector before any of the extra sensor related stuff is started. Apparently building inspector won't be getting involved in the CU debate, it's down to the electrician's governing body so that's thrown up another question?
 
Hi - there would seem little point in replacing that Consumer Unit. But they are not that expensive. If it's being relocated it will involve the same testing IMHO as replacing so you could consider it I suppose. I'd confirm the brand and type of detectors planned, as there are £10 ones and £60 ones, just saying.
 
As I said before, nothing wrong with that board, it's a better quality one than they would more than likely install and there's no need to update as it's only being moved. Not as if it's an old 3036 board.
 
What are the schemes take on 'moving' a consumer unit?
It will involve the same work as replacing old for new, so should involve the same testing of cables and connections.

If it was just moving a couple of inches to fit in another piece of equipment, then no disconnection taking place, no need to update board or test.

Its this individual electrician's understanding of the regs.
 
So all the guys on here stating they would not change the board what certificate would you provide?
Because you wouldn’t be able to provide an installation certificate
For the cost of a new easy 9 board without breakers it is a no brainier

The smokes he is rong but you can’t beat hard wired for reliability what price on your family’s life
 
From my experience on the few extensions, I have been involved with building control have wanted smoke detectors on the escape route and heat detectors in the kitchen.
 
Mini-update-
From tomorrow, 1st March, the regulations change in Scotland, allowing the fitting of 10 year tamper-proof battery alarms, smoke and heat, linked by a wireless connection/radio module, in rented property, where previously hard-wired alarms were required.
 
Thanks for the input guys, very much appreciated. Builder has said he's checked with building inspector and the inspector wants to see minimum 2 x mains wired smokes. The heat and CO he's not bothered about apparently. Weird!

The cost associated with moving the Consumer unit is at the interpretation of the electrician based on his governing body and he's not changing his mind on that. He still says we need a new gen-18 metal box.

Sounds like building inspectors have there own interpretations as I'd been given advice from LA building control that wired mains detectors weren't required. The builder is using a private building inspector company.
 
On the face of it there's no requirement to swap out a perfectly good distribution board. It may not be the very latest but is still fit for purpose and a very good make.

As for smokes/heat/Co detectors etc as I'm guessing yours is a private property then there's no requirement for mains powered devices although they are my preferred option.

Has the electrician mentioned membership of any scheme such as NICEIC/STROMA/NAPIT etc?

I would seek quotes from another two electricians, if you know anyone that could recommend one then great if not post up a rough location then I'm sure a forum member would be close by and able to quote for you.
How can you tell from the photo whether the consumer unit is made out of metal??
 
CU is moving about 6ft up the wall it's currently fixed to, mains cable runs up the same wall.

We've not anticipated any circuits being extended as the current rooms already have lights, sockets, oven etc. circuits in them. There will be some moving of wiring but doubt there'll be additional circuits needed. There are 3 spare module slots in the current CU if that makes any difference.
So why is the consumer unit being moved up the wall?
 
Hi There,

New to the forum and come across this. I am not an electrician but a builder and relating to your query regarding the smoke/heat detectors I can only tell you this.

When we've been completing any works regarding new extensions, alterations or conversions (in most cases for us this is extensions and alterations for installation of new kitchen/diner areas) the requirement has always been to install a heat detector in the kitchen area, smoke detector in dining area and interlinking smoke detectors to the rest of the property (this is to be mains fed with a battery back up).

The referencing for these requirements can be found within 2 areas Approved Document B (B1) and forms part of Part P (10.2.2 (specifically (c)&(e)).

I have always been queried by prospective clients on this issue, to show them that I am not pulling the wool over their eyes and trying to charge more, I keep 2 specific guides with me at all times these are:-

IET On-Site Guide BS7671:2018.

IET Electricians Guide: Electricians guide to the Building Regulations.

They are a quick go to guide for the clients to see what is expected.

On another note, Regarding moving the CU 6ft higher, my only concern is the fact that it is being moved to a location above a fridge (I assume either a tall unit or at least a fridge freezer), would you consider moving it to another "Local" area where if there are any issues the CU can be easily accessed. Imagine this fridge on fire, no way of isolating and when the fire service turn up and start squirting water they're going to adding water to area with a Live CU above it, just saying.
 
Thanks for the input guys, very much appreciated. Builder has said he's checked with building inspector and the inspector wants to see minimum 2 x mains wired smokes. The heat and CO he's not bothered about apparently. Weird!

The cost associated with moving the Consumer unit is at the interpretation of the electrician based on his governing body and he's not changing his mind on that. He still says we need a new gen-18 metal box.

Sounds like building inspectors have there own interpretations as I'd been given advice from LA building control that wired mains detectors weren't required. The builder is using a private building inspector company.
so -called "governing bodies" do not make the regulations. the IET do. these are in BS7671, and you need to get this electrician to bring his copy and show you the regulation that says he's got to replace the CU. he'll never find it, as there isn't one. then tell him to FO.
 
so -called "governing bodies" do not make the regulations. the IET do. these are in BS7671, and you need to get this electrician to bring his copy and show you the regulation that says he's got to replace the CU. he'll never find it, as there isn't one. then tell him to FO.
Out of curiosity what certificate would you complete for the CU move ?
 
Out of curiosity what certificate would you complete for the CU move ?
strange one here.no new circuits, so EIC not necessary. all circuits modified, if extended them MWC for each altered circuit, or.....

hit it with a hammer. if it still works, it's ok.
 

Reply to Mains wired smoke / heat / CO detector question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Been covered before, but wondering if any amendments recently. I’ve been asked to fit detectors in a bungalow holiday cottage. Just over the...
Replies
0
Views
668
I currently have a home with 7 interconnected, hard-wired smoke detectors. I have a hard-wired heat alarm in the garage that I need to have...
Replies
4
Views
2K
I've asked a similar question before I think and we came to the conclusion that apart from new houses and HMO's etc there aren't any rules about...
Replies
3
Views
364
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Hi all Recently we've been having a few issues with smoke and heat detectors.. been fitting them for years and years now mostly without any...
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock