Discuss Max amps from UK socket in the UK Electrical Forum area at ElectriciansForums.net

damunk

-
Reaction score
2
I have been told I can use a 30Amp welder from a normal UK socket.

But I have seen numerous posts that say 13amp is max from single socket and 20AMP is max from double socket:

I must be missing a trick. Some internet postings below.

"Double sockets are rated for 20A draw, over this long term will burn the socket out, so 2 x 13A long term and you might have problems."

From google main page:
Most modern residential circuits are 15 or 20 amps, so we're looking at a max load of either (15A x 120V =) 1800 watts or (20A x 120V =) 2400 watts before the breaker trips. The breaker will be labeled either 15 or 20.

Each socket (presumably for flat pin plugs) is designed to deliver a maximum of 13 amps - hence the 13 amp fuse you find in new plugs. Thus a double socket can supply no more than 26 amps.

Another direct link: IET Forums - 13 amp twin socket outlet - http://www.------.org/forums/forum/messageview.cfm?catid=205&threadid=33787
 
But I got this direct from mig welders forum:

"uk households are 240v 32amps on your plugs the 13amp plug can be used with the clarke 151 no problem at full power

i also have the plasma cutter cut 50 and have run that on a 13 amp plug with 45amps

so you will be fine on most plug systems"
 
Well............ there we go, contradictory information.

Websites do offer a lot of it.

Best you ask the manufacturer what is required.
 
does the welder have a fitted plug? if so, then it's designed to fit into a comparable socket. the current rating shown for the welder is the output current (at a lower voltage). you need to determine what the full load current is @ 240V.
 
But I got this direct from mig welders forum:

"uk households are 240v 32amps on your plugs the 13amp plug can be used with the clarke 151 no problem at full power

i also have the plasma cutter cut 50 and have run that on a 13 amp plug with 45amps

so you will be fine on most plug systems"

Sorry to say, but "an anonymous welding guy on a web site said it was ok" probably won't wash with your insurance if the worst happens ... As @telectrix says in #8, the clue is what plug Manufacturer has put onto the welder originally.
 
The specifications for the welder state that it can supply 150A at 21V so this would be 13.7A at 230V plus any losses in the system. The instructions state that the welder has a standard 13A plug.
These welders are fitted with a standard 13 amp BS 1363 plug, fitted with a 13 amp fuse. Connect to a 230 volt (50Hz) domestic electrical supply and we strongly recommend that this be done via a Residual Current Device (RCD).
Overall you should be OK, but I would not recommend using it for a long while at full pelt.
 
As Richard said ^^^^^
You won't have a problem using this welder on a domestic socket circuit. Though as he mentioned, using it for a long time on full power would not be recommended.

150amp single phase mig-welders are not much use for any sort of long term fabrication work, you won't be able to successfully weld anything much thicker than 3mm. They are mainly design for a bit of tin bashing, like patching up cars and stuff like that. If this is all you intend to use it for it will be fine.
 
Double sockets are not intended for continuous use at 2x13A, although they should not immediately burn out if subjected to this. Good ones might last the course. But the issue is the circuit wiring - unless you know how the circuit is laid out, you can't tell whether the point load of the welder and the three vacuum cleaner motors will overload one leg of a ring circuit, or trip the MCB. Your load is not a typical domestic one and should have preferably dedicated circuits - welder instructions often specify a higher-rated circuit than their apparent requirement, so that you don't get nuisance trips from the momentary peaks and overloads that they tend to produce, and the inrush when switching on.

No wonder you were after stabilisation for the motors - running a welder at the same time on the same circuit will drag the voltage all over the shop due to cable voltage drop.

BTW the reference to 15 or 20A breakers is for American 120V circuits!
 
From the ebay seller that is selling the unit:

"No this welder will not run on full power from a 13amp supply it would require 16amps. So it will not be able to run from a domestic 13 amp plug supply."
 
fit a second cable and plug top to the welder. then plug each of the 2 plugs into separate sockets on different circuits. this will then split the current between circuits.

N.B. DO NOT TRY THIS AT HOME, I'S A JOKE..
 
fit a second cable and plug top to the welder. then plug each of the 2 plugs into separate sockets on different circuits. this will then split the current between circuits.

N.B. DO NOT TRY THIS AT HOME, I'S A JOKE..

I know a "welder" that did just that and made them for his mates!!!
 
From the ebay seller that is selling the unit:

"No this welder will not run on full power from a 13amp supply it would require 16amps. So it will not be able to run from a domestic 13 amp plug supply."
Is the seller a welding supply specialist?
Because welders have what's called a "duty cycle" this means that you should only operate the welder at full power for a certain time ratio. This ratio depends on the power setting of the welder.

Below is the spec sheet for the welder you have posted about, note that the rating of the input supply fuse is 13A. The duty cycle ratio is quite low at under full power @ 15% this means that for 9 minutes welding there should be a down time of 51 minutes. I doubt you would need to hard wire this machine unless you intend to do lots of welding within a short time at full power. If so I would say that this machine is not suitable for your requirements anyway.

230V 50Hz 1Ph


Fuse Rating 13Amps

Current Range 30-150A

Max. Metal Thickness 3-5mm

Welding Wire Sizes 0.6-0.9mm

Duty Cycle*

15% - 130A

60% 62A

100% 48A

Dimensions 700X320X580mm


Weight 25kg




 
sod all that techo crap. can you come and weld me up my rear sill what some woman driver kindly bent for me?
 
Get plenty of flap discs for your grinder, I have similar and they spread spatter like mad!!!
 
At David M. I am only welding 3mm and its is just a small project. Building a frame out of box section thats all. 3mm box.
In my opinion you will be fine using this welder the socket circuit for this job then. Gas less mig welding isn't as neat as using argon. But if you intend to dress up the welds after you should be just fine.
 
The Clarke are ok welders .top setting will blow your 13a fuses after a few minutes , but to weld 3mm not a problem . Spend a few quid and get it converted to a eurotouch, as the torch it comes with is not the best
I agree, I have a 180amp mig that popped fuses if I used it for too long a period of time. I've now hard wired it on its own dedicated circuit rated on a 16mcb and its been no trouble since. The standard touches are rubbish! the euro ones are definitely worth investing in.
 
Right. Thanks for the help on the welder.

The three motors are for a air flow bench i've built. They are all wired up to one motor controller unit.

From the motor controller unit, one cable to the wall outlet.

The motors are 240V 5amp. Will this be okay?Or I need to separate the feed into three so to use three sockets?
 
This is a guess . Do the motors pull 5amps , if not good but if switched on at the same time the peaks may do . You could fit overloads to protect each motor and a stop start circuit for each motor to be able to delay the start of each motor from each other (you could design a timer to start motor 1 then motor 2 etc and just use one stop start ) . Fit estop transformer contractor etc. ) . Before even thinking about this amp test the motors
 

Reply to Max amps from UK socket in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I am trying to understand how a relay system works and have designed a circuit and a ladder diagram all as attached for an 8 PIN relay, a current...
Replies
14
Views
597
Hi I have a 1 bedroom appartment from 1954. I opened my breaker box to find out what the extra double 20 amp was used for and I realized that it's...
Replies
1
Views
661
The garage is 17 mtrs x 15 mtrs in the UKh The house has a 100 amp supply to the house consumer unit. The garage consumer unit is fed from a...
Replies
4
Views
1K
I’m running wires to the basement for future basement finishing. I’d like to add two circuits of outlets (one on the finished side and one on the...
Replies
1
Views
699
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock