Discuss Max demand for double oven and hob in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
52
Just some clarification please.

Max demand for cooking devices.

OSG says 10A + 30% of "connected cooking appliances in excess of 10A + 5A" if a socket is available in the isolator. The oven and hob are two devices. Does the 15A apply to both of them or just the first one?

eg: Oven 4.8 kW Hob 5.5 kW. With a socket available.

15A + (((0.3 x 4.8) + (0.3 x 5.5))/230) = 28.4A

or

15A + ((0.3 x 4.8)/230) + 15A + ((0.3 x 5.5)/230) = 43.43A

Thanks in advance
 
Just some clarification please.

Max demand for cooking devices.

OSG says 10A + 30% of "connected cooking appliances in excess of 10A + 5A" if a socket is available in the isolator. The oven and hob are two devices. Does the 15A apply to both of them or just the first one?

eg: Oven 4.8 kW Hob 5.5 kW. With a socket available.

15A + (((0.3 x 4.8) + (0.3 x 5.5))/230) = 28.4A

or

15A + ((0.3 x 4.8)/230) + 15A + ((0.3 x 5.5)/230) = 43.43A

Thanks in advance
Good question, not sure will ask around, Personally I would say the hob and the Oven are qne cooking device, some of the active members may be able o provide an answer.
 
First and foremost I'd refer to connection instructions for both appliances. I'd personally want a circuit for each of those appliances.
 
First and foremost I'd refer to connection instructions for both appliances. I'd personally want a circuit for each of those appliances.
So a seperate MCB for each? Not unreasonable but I have never seen it. Friend of mine has just had an old house completely rebuilt and rewired. Including new kitchen. Oven and hob are connected to the one B32. Treating them as one device only comes to 29A with 11kW full load.
[automerge]1594642457[/automerge]
Good question, not sure will ask around, Personally I would say the hob and the Oven are qne cooking device, some of the active members may be able o provide an answer.
Treating them as one device only comes to 29A with 11kW full load. So that woud be fine.
 
So a seperate MCB for each? Not unreasonable but I have never seen it. Friend of mine has just had an old house completely rebuilt and rewired. Including new kitchen. Oven and hob are connected to the one B32. Treating them as one device only comes to 29A with 11kW full load.
[automerge]1594642457[/automerge]

Treating them as one device only comes to 29A with 11kW full load. So that woud be fine.

Yes I always try and divide the installation as much as possible. I have been known to add 6 new circuits on a kitchen fit.
It may be fine diversity wise. You can get a double outlet plate if doing this. The manufacturer's instructions for each appliance may say to connect to a dedicated 32A circuit though so worth checking them out and taking that into account in your design.
 
Yes I always try and divide the installation as much as possible. I have been known to add 6 new circuits on a kitchen fit.
It may be fine diversity wise. You can get a double outlet plate if doing this. The manufacturer's instructions for each appliance may say to connect to a dedicated 32A circuit though so worth checking them out and taking that into account in your design.
A totally get that to be honest. When I first encountered the diversity rules I found the probability aspect of the diversity calcs a little uncomfortable but I understand why it's done that way. It takes into account the intermittent nature of thermostatic controls. It keeps the costs down and costs are important at the end of the day. I know of one socket circuit in a commercial kitchen that has 16 13 amp outlets on a B32.
 
I would be happy to have both appliances on one MCB (32A) with one isolation switch (as long as both oven and hob are close enough to each other to maintain local isolation) and a dual cooker outlet plate.

As for diversity, I would treat them separately. It doesn't make sense to me to treat them as one item as they are not. If one item is on full there is no limiting device to make sure the other is not. However, if there is only one isolation switch with a socket outlet then the additional 5A (with regards diversity) is only added once.

Oven = 4.8kW = 21A.
Diversity = 10A + (0.3x11A) = 13.3A

Hob
= 5.5kW = 24A.
Diversity = 10A + (0.3 x 14A) = 14.2A

max demand = 13.3A + 14.2A + 5A(socket) = 32.5A

I realise the max demand is 0.5A over the 32A MCB but as I have rounded up the initial current for both appliances I would say it's OK. You could fit a 40A MCB assuming using 6mm cable and acceptable reference method.
 
Last edited:
as above comments. up to 15kW cooking appliance on a 32A circuit is fine has been for donkeys years. wrt Andy78's post, putting them on separate circuits is a good idea though, purely for the fact that if 1 appliance has a fault and needs to be isolated, the other one will still be usable. depending on which one can still be used, you have a choice of oven chips or chip pan chips.
 
In addition....

Ps.. Well done with all your correct, yet perhaps OTT brackets in your OP :D

Pps.. I'm not quite sure of your maths though.

Remember the 30% is only taken from the 'excess' current.

e.g if the oven is 4.8kW = 21A, the 30% is only taken on 11A of that as you have already taken off 10A as a fixed amount. So diversity for that one appliance is the first 10A + (30% of 11A) = 13.3A
 
In addition....

Ps.. Well done with all your correct, yet perhaps OTT brackets in your OP :D

Pps.. I'm not quite sure of your maths though.

Remember the 30% is only taken from the 'excess' current.

e.g if the oven is 4.8kW = 21A, the 30% is only taken on 11A of that as you have already taken off 10A as a fixed amount. So diversity for that one appliance is the first 10A + (30% of 11A) = 13.3A
Thanks for the response.

Brackets are a great way to get around BODMAS. Makes life easier. For me at least.

Ok. "in excess of". I didn't factor that in. That's true. I forgot to do that. But I think you'll find that the maths is fine in my calcs given the values I have used.

This post does seem to illustrate that there can be a variation in this calculation depending upon how you view the arrangement. My original question was about how you interpret the rule. The one appliance vs the two appliance perspective.

Anyway, whatever comes out of the calculation I think if I get up on Christmas day, put a pan of vegetables on each of the hob plates, a turkey in the oven and turn everything on the actual demand is going to be about 45A for about 5 minutes. Nevertheless the existing B32 should be ok. It's class B so it trips at a minimum of 96A.
[automerge]1594652236[/automerge]
In case anyone is wondering, I have an electric oven and a gas hob. I am pulling the gas hob out and replacing it with an electric hob. Hence the question.
 
Gas Hobs Rule--- OK. only reason to swap for leccy one is:
1.you want an induction hob as it's maybe more efficient.
2. your missus wants one coz next door just bin bragging about theirs.
 
I only recently got to grips with BODMAS...that's why my biomass boiler is 18x bigger than I needed.
Induction hobs...there is no finer way to cook...IMHO. Especially if you have no gas supply.
 
I only recently got to grips with BODMAS...that's why my biomass boiler is 18x bigger than I needed.
Induction hobs...there is no finer way to cook...IMHO. Especially if you have no gas supply.
Perhaps. But I just checked. They're twice the price and I'm not sure my man pan is compatible. They reckon they are but I'll keep it old school. Might get a second hand one even. See how it goes.
 
As for diversity, I would treat them separately. It doesn't make sense to me to treat them as one item as they are not. If one item is on full there is no limiting device to make sure the other is not.
It does make sense to treat 2 (or more) cooking appliances as one when applying diversity. After all, diversity relies on there being several 'elements', with not all of them being on full simultaneously. The more parts there are, the more valid diversity becomes.

You make a very good point about the internal power management of some cooking appliances though. In these instances, I believe it is correct to use the 'sum of the parts' and apply diversity to that, rather than applying it to the appliance rating.

For example, supposing the OP's hob was a 4 zone induction hob, each zone rated at 3.2kW, but internal power management limits it to 5.5kW. The sum of all the zones is 4 X 3.2 = 12.8kW, this is the figure we would use to calculate diversity, not 5.5kW.
 
It does make sense to treat 2 (or more) cooking appliances as one when applying diversity. After all, diversity relies on there being several 'elements', with not all of them being on full simultaneously. The more parts there are, the more valid diversity becomes.

You make a very good point about the internal power management of some cooking appliances though. In these instances, I believe it is correct to use the 'sum of the parts' and apply diversity to that, rather than applying it to the appliance rating.

For example, supposing the OP's hob was a 4 zone induction hob, each zone rated at 3.2kW, but internal power management limits it to 5.5kW. The sum of all the zones is 4 X 3.2 = 12.8kW, this is the figure we would use to calculate diversity, not 5.5kW.
Just watched the JW video you posted. It's a pretty recent one. He produces great vids. I have watched loads of them. That's the way to go.
[automerge]1594669816[/automerge]
Better to have redundant brackets in an expression than the wrong answer from not remembering precedence-order perfectly!
I'm a retired computer programmer. Thirty years in the biz. Brackets in formulae are essential when writing code.
 

Reply to Max demand for double oven and hob in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm interested what people's gut reaction solution would be. Kitchen design and customer said freestanding cooker. So I first fix 10mm, and boxes...
Replies
30
Views
3K
Hi Guys, I am just changing my plug top oven over & gas hob and noticed the following: 32AMP Breaker > 6MM Cable > Cooker Switch 45a > 4mm cable...
Replies
2
Views
2K
Hi there I have a few questions related to the power ratings of certain devices and how this interplays with the fuse. The reason I am asking...
Replies
4
Views
974
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
I've just spent an hour getting bogged down with the maths trying to work out diversity for 2 cooking appliances on the same circuit (32A MCB)...
Replies
36
Views
16K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock