Hi guys,

Just doing an EIC for a recent dis board change, I also installed a 50a (type b 60898) shower circuit for an 11.5KW shower. I am looking through my regs trying to find whether it comes under the 5s disconnection time...? I know 0.4s is for circuits less than 32A and non-distribution circuits, so from that I would conclude that the shower is 5s, but I have heard because it is in a special location, it comes under 0.4s. Is this true? Have looked through 411.3.2.2 and also the special locations section but nothing immediately jumps out at me regarding this.

Any help would as ever be much appreciated :)

Toby
 
60898 disconnection time from 0.1 to 5 sec are the same for a fault current 5x it's current rating on the chart so it Don't matter.
 
the RCD should dis. within 300mS. but it's the max. time allowed, he's asking for.
 
Whats the maximum disconnection time for when "the wife" is taking a shower

5 secs a tad harsh do you think
icon7.png
 
RCD in irrelevant. the disconnection time required relates to a fault of negligible impedance L-N or L-E. the disconnection time should be met by the combination of PFC and the OCPD. the RCD only comes into the equation on a TT system where dis. times can't be met otherwise. the RCD is there for additional protection on a TN system.
 
5 second disconnection times are for distribution circuits protected by fuses of whatever number. BS60898 mcb's have the same max Zs values for 0.4 and 5s disconnection, times its all in the appropriate tables in both BGB and OSG.

Cheers..............Howard
 

Reply to Max disconnection times for 50a shower circuit ? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Bathroom with an electric shower wired to the latest regs with a 40A MCB and RCD protection. Is the disconnection time 0.4s or 5s. Looking at the...
Replies
15
Views
3K
Hi all. Sort of an interesting one. I had a call from a client to say she is getting a shock when using the shower. I told her not to use it and...
Replies
15
Views
2K
Hi, I`m looking for an advice. I have an electric shower that I`m not using due to boiler changed to combi and added shower over bath feed by a...
Replies
1
Views
949
Legends, need some advice. I am a 12v automotive electrician, but have had a side project building a concession trailer for my dad. We have an...
Replies
6
Views
806
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
539

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top