Search the forum,

Discuss Max floor area of a ring main? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

C

Crosswire

I always thought that you were allowed "unlimited socket outlets within 100m Sq."

I got told today that if the floor area was above 75m Sq it required an addittonal ring and this was the "new Regs" .

Is this correct?
 
BG will tell him it's dangerous and needs replacing, before putting the socket tester away.
 
is this helpful.. 75sq.m. = bullsh!te. IMO.
 
Just to be helpful - nothing has changed with 'historical' rec's - but that has been frowned upon by anyone who is familiar with modern demands on a ring. I'ts not rocket science to know that as telectrix says, it's bull. Use initiative and calcs.
 
Hi Crosswire
As you can probably tell, the general consensus here is that the info you've been given is bull poo.
is there a job you're on with more than said floor space? also, who told you this duff info?
 
Just to be helpful - nothing has changed with 'historical' rec's - but that has been frowned upon by anyone who is familiar with modern demands on a ring. I'ts not rocket science to know that as telectrix says, it's bull. Use initiative and calcs.

Thanks for that, I though so but wanted confirmation
 
Hi Crosswire
As you can probably tell, the general consensus here is that the info you've been given is bull poo.
is there a job you're on with more than said floor space? also, who told you this duff info?

It was another sparks on the job who is putting two general rings into a 3 bed flat that has atotal of 12 double sockets, on the basis that the floor area is 84 sq meters. (also kitchen ring, so three in total)
 
I always thought that you were allowed "unlimited socket outlets within 100m Sq."

I got told today that if the floor area was above 75m Sq it required an addittonal ring and this was the "new Regs" .

Is this correct?

There used to be guidelines many moons ago, but i cant remember what they were, and they are irrelevant now anyway.
When you construct a ring (or any other circuit), you need to consider the loading, so if you were to install a ring into 4 bedrooms, and put 4 twin outlets in each room, and SFCU for a boiler or whatever, you wont have problem with loading, no matter how many tellys, laptops etc etc gets plugged in, you will not exceed the cable rating. But put a kitchen, utility room, garage on one circuit with unlimited outlets than you may encounter problems.

It all comes down to using a bit of common sense, and looking at the info available to you. If you look in the electricians guide to the building regs, there are guidelines as to how many outlets you should provide in each location, but they are only guidelines. You need to consider inconvenience in the event of a fault, so would it be a good idea to shove a 125m ring in? i doubt it, cos all the sockets might go off at once. You are correct in your assumption that you can have unlimited sockets on a ring, you can on a radial as well, but it all comes down to common sense. You can also spur from each unlimited socket once. When you design and construct any circuit, you need to ensure compliance to the regs, so think about Zs values and volt drop when calculating the length.

Cheers..........Howard
 
There used to be guidelines many moons ago, but i cant remember what they were, and they are irrelevant now anyway.
When you construct a ring (or any other circuit), you need to consider the loading, so if you were to install a ring into 4 bedrooms, and put 4 twin outlets in each room, and SFCU for a boiler or whatever, you wont have problem with loading, no matter how many tellys, laptops etc etc gets plugged in, you will not exceed the cable rating. But put a kitchen, utility room, garage on one circuit with unlimited outlets than you may encounter problems.

It all comes down to using a bit of common sense, and looking at the info available to you. If you look in the electricians guide to the building regs, there are guidelines as to how many outlets you should provide in each location, but they are only guidelines. You need to consider inconvenience in the event of a fault, so would it be a good idea to shove a 125m ring in? i doubt it, cos all the sockets might go off at once. You are correct in your assumption that you can have unlimited sockets on a ring, you can on a radial as well, but it all comes down to common sense. You can also spur from each unlimited socket once. When you design and construct any circuit, you need to ensure compliance to the regs, so think about Zs values and volt drop when calculating the length.

Cheers..........Howard

I agree with everything you have said, except for unlimited sockets on a radial circuit.
 
How standards have dropped!!, any experienced sparky I hope would not wire 12 s/o 0n 20 amp radial on 2.5mm cable.so you would say that's good practice then?
 
How standards have dropped!!, any experienced sparky I hope would not wire 12 s/o 0n 20 amp radial on 2.5mm cable.so you would say that's good practice then?

yeah ?
well where did you get your numbers from ?
only 2 on a radial ? dont be daft.
seeing as the circuit device will prevent cable overload there is no maximum.
 
What's happening this evening, it must be the high pollen count. Some of these posts this evening are bordering insanity, why don't we just prevent the customer from using electricity just incase they alter something.

Give it a break, work to the regs and let the rest of the world go by.
 
I always thought that you were allowed "unlimited socket outlets within 100m Sq."

I got told today that if the floor area was above 75m Sq it required an addittonal ring and this was the "new Regs" .

Is this correct?

if you have a look in onsite guide (amendment 1)

100m is the recomended max length for a 2.5 ring feeding sockets.

also mentions 50m for lights if i remember correctly, havent used onsite guide for a while
 
Rumour has it that the next BS7671 recommends that socket outlets be wired in 16mm T&E, be protected by a 6A breaker and the total number of SO's be limited to 0!
 
Surely if you only put 2 SO on a radial with a 20a breaker, there is FAR more likely hood of mr DIY adding sockets thus creating the circuit you fear so much, oh and he can also change the breaker to a 63a so why ain't you wiring in 16mm ' just in case'
 
Surely if you only put 2 SO on a radial with a 20a breaker, there is FAR more likely hood of mr DIY adding sockets thus creating the circuit you fear so much, oh and he can also change the breaker to a 63a so why ain't you wiring in 16mm ' just in case'

Theres nothing stopping any numpty changing a breaker so that's a non starter - you can't legislate for the idiots, nor can you be held responsible for DIY antics later.
 
Last edited by a moderator:
if you have a look in onsite guide (amendment 1)

100m is the recomended max length for a 2.5 ring feeding sockets.

also mentions 50m for lights if i remember correctly, havent used onsite guide for a while

Okay guys, we need to put this one to bed. It's not "100m is the max length for a 2.5 ring feeding sockets." It's Maximum FLOOR AREA per 100 square metres. In the BGB they clearly state that "Historically, a limit of 100 square metres has been adopted". This is where the "ring final circuit starts and finishes at the distribution board, where it is connected to a 30A or 32A overcurrent protective device".

It is clearly a recommendation (historical). 433.1.103.
This can be achieved by:
(i) locating so's to provide reasonable sharing of the load around the ring.
(ii) not supplying immersion heaters, comprehensive electric space heating or loads of a similar profile from the ring circuit.
(iii) connecting cookers, ovens and hobs with a rated power exceeding 2 kW on their own dedicated radial circuit.
(iv) taking account of the total floor area being served. (historically , a limit of 100m squared).

And it's not 50m length for lights - It's, for a Radial final circuit with a 20A protective device in 2.5mm (historically the floor area served is limited to 50m squared)

And for a Radial final circuit with a 30A or 32A protective device in 4mm (historically the floor area served has been limited to 75m squared.

I probably muddied the waters with my tongue in cheek comment that "mr diy would come along and uprate the breaker" This was meant as a throw-away quip - but obviously some peeps have taken it as verbatim. For that I apologise. I'll be more careful in future with my attempts at comedy.

I ought to add that the above quoted Regs are not aimed at the many regulars on here who are familiar with them - But those who may not have updated may find them helpful.

Ok, I'll put my tin hat on.
 

Reply to Max floor area of a ring main? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Ok. Can you cut a ring in half, add junction box, then run a spur off it? I thought it had to be from a socket? Mate of mine wanted me to see if...
Replies
3
Views
813
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
977
Hello, I bought a new build and noticed the upstairs MCB is controlling some sockets on the opposite floor, so if I flick the upstairs MCB it's...
Replies
31
Views
2K
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
806
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
522

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock