Discuss MAX Ze value for TT? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
36
Hi,
I'm in my second year at college, but I'm a bit unclear on what the max Ze should be for a TT system. I know that the regs say 200ohms, and my tutor said that it would be acceptable if you found an earth rod which gave a reading of 200ohms. However several of my mates who have been qualified for years, tell me that they don't agree. They won't certify a TT install if it has a Ze of more than 20ohms?

What's everyones opinion on this?

Thanks in advance. :)

Toby.
 
Last edited:
They won't certify a TT install if it has a Ze of more than 20ohms?

that's crap. unless you use 2 5/8" rods screwed together, you'll be very lucky to get under 100 ohms. this 20 ohms comes from a misunderstanding confusion over DNO earthing max. of 21 ohms. all TT systems must be backed up with 30mA RCD on all circuits so the max Zs for any circuit is 1667 ohms.
 
The earth path is made up of several sections

1/ The suppliers earth electrode , usually quoted as 21 ohms max.

2/ Resistivity of the soil, could be as high as 20k ohms

3/ the contact resistance between the installation electrode and the surrounding ground, this is where you come in as the sparks.

The maximum Ze allowed by the IET is 200 ohms, NICEIC = 100 ohms,
 
How come the NICEIC require 100ohms, when the regs state 200ohms?

because the niceic think that they're God. superior to the IET, so much so that they endorse a visual inspection of an installation , when 90% of sparks do proper test/inspections
 
Last edited:
How come the NICEIC require 100ohms, when the regs state 200ohms?

because the niceic think that they're God. superior to the IET, so much so that they endorse a visual inspection of an installation , when 90% of sparks do proper test/inspections

I can't understand why the IET have chosen 200 Ohms when its obvious why 100 Ohms was chosen by NICEIC

Zs = 50 / 0.5

Why 50V, lets say touch voltage
Why 500mA , Lets say maximum acceptable current rating of a domestic/commercial RCD providing the maximum earth fault path resistance for instantaneous disconnection under the 16th ed. BS7671

I suspect that the NICEIC will be updating their advice soon.....
 

Reply to MAX Ze value for TT? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Replies
18
Views
2K
Hope this all makes as much sense as i can make of it and my "problem" can get sorted via some guru on here... Just a quick background on myself...
Replies
4
Views
1K
Hi all, Just wondering if anyone can shed some light on the max zs values in the OSG, they don’t seem to follow the 1.25 divisor stated in the...
Replies
10
Views
8K
Hi everyone, I'm new here and was wondering if someone could help to get my college project calculations right. I'm about to start my 2nd year in...
Replies
12
Views
8K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock