Morning all,

I'm currently finishing off my Lvl 3 C+G and I just need to finish off my design spreadsheet then I'll have completed it. I've one last column to fill in "Max Zs @80%" the design is based on a hotel using a TN-C-S supply. I'm just wanting to know where I can find this information in the On Site Guide.

Thanks
 
You can use the values from Tables 41.2 to 41.4 in BS7671. Just calculate the 80% value from those.
 
The values in the OSG for max Zs are already adjusted. As Westy said regards BS7671 you have to multiply those by 0.8
 

Reply to Max Zs @ 80% TN-C-S System in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Now Ive done Periodic Inspection and Initial Virification Qualifications with LCL/EAL (so non C&G 2394/95) # strange part building Modules , this...
Replies
6
Views
1K
all currently working towards my 2391 c&g I&T . I know how to calculate v.d. but the mock test I found online seems a bit out of date or I'm...
Replies
2
Views
825
Afternoon all, Got a bit of a strange one (by my usual standards anyway). Job is a large barn conversion, done years ago, there's loads of work to...
Replies
6
Views
1K
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
1K
I am installing a Victron Quattro in an island mode configuration (in the UK, the DNO is the NG). I will be adding a stand-by generator. My...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top