Hi

Would anyone be able to help me,
Max zs value for type c 32amp RCBO on PME system- 0.72/0.58 or 1776 ohms?

Any help would be appreciated
 
The RCD element of the RCBO is their as additional protection on a PME system. You need to meet the disconnection times for the MCB element.
 
The RCD is additional protection only. What would happen if the RCD failed? Whilst they are great as additional protection, they should not be relied upon as the sole means of protection, as you effectively would be doing if you went with such a high Zs figure! The MCB would become basically just a switch!
 
you need to design the circuit so that the max. Zs is as specified for the OCPD, but there's nothing to say you can't enter 1667 in your SOTR.
 
This i suppose very much depends on whether this is a ''New Circuit'', or an existing circuit that's been altered etc. It seems if existing it's OK to rely on the 1667 ohms of an RCD!! Not my way of doing things, i might add, i would always find the reason for exceeding Max Zs and rectify as needed/required. But if this is for say, a periodic test report purpose, going by BS7671 the circuit conforms as such!!!!! lol!!
 
Agree with previous post. The RCD is there for additional protection, correct installation methods being meet would mean correct/complying Zs values. Don't use RCD's as a cheat to justify high Zs readings, Investigate as there could be loose connection etc......
 

Reply to Max Zs value in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Any ideas on the Max Zs on a 3871 Type 3 13 amp MCB
Replies
10
Views
1K
Hi everyone, Happy Friday! Could someone please point me in the right direction, I’m after the Max Zs for a Bill Talisman TLF633 63A MCCB, I’ve...
Replies
4
Views
1K
hello , can anyone reccomend a free download for max zs values for bs 3871 ct breakers please
Replies
2
Views
1K
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
785
Hi All, Just looking for some advice: I'm in the process of updating an old cable calc spreadsheet that helps to spit out Zs and Voltage Drop...
Replies
8
Views
920

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock