The generator when tested produced a fault current of 2.8Ka
The generator is running prime.
The generator has been serviced every 450hours
I have recently started working for this company after 14 years in fixed wiring, but maybe it doesn’t transfer over like fixed wiring?
Is that the actual measured current under fault conditions? Or is that the fault current given by a test meter after a Zs test?
It’s not completely different to fixed wiring, but there are extra considerations with generators.
Generators react to the load applied a lot more than a supply from the DNO does. The DNO supply has several massive alternators in power stations across the country keeping it stable, the generator has just its own engine and alternator.
The engine will slow down when a large load is applied, so they can rarely deliver large instantaneous currents, it takes time to speed up the engine.
You can kind of relate a short circuit to trying to pull away in 5th gear , it don’t like it and will probably stall.