On a generator that value is not much use, that meter calculates the value it doesn’t measure it. It doesn’t take in to account any of the characteristics of the alternator or the engine.

So how do I know that I am going to achieve disconnection times required?
 
So how do I know that I am going to achieve disconnection times required?

You’ll need to characteristics of the generator to establish the available fault current by calculation or from the data sheet for the generator.
For all the generator setups I am involved with I use variable earth leakage relays to achieve fault protection.
 
I’m going to embarrass myself here and ask what a rubber box is.

?

Great posts from Davesparks btw.

Just like a waterproof box with sockets mounted on it.

2444EDCE-CA7E-418B-BBE5-8D19812A6A1E.jpeg
 
I’m going to embarrass myself here and ask what a rubber box is.

?

Great posts from Davesparks btw.

Rubber box is a company who manufacture distribution units (usually referred to as distro) for temporary installations, usually made of tough rubber.
The term rubber box has come to mean any rubber distro, much the same as vacuum cleaners being referred to as hoovers.
 
You’ll need to characteristics of the generator to establish the available fault current by calculation or from the data sheet for the generator.
For all the generator setups I am involved with I use variable earth leakage relays to achieve fault protection.

Out of interest, how do you protect against Line to neutral faults?
 

Reply to Maximum zs generator and rubber box in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
567
I am interested in having a home generator that would provide power to my home when the power is out during hurricane season, etc. I have 2...
Replies
0
Views
315
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
837
Hi, i live in a new build house where they builders have left a junction box on the outside of my house. In the junction box there is a 6mm twin...
Replies
14
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock