Discuss Metal bathroom cabinet with inbuilt shaver socket not earthed in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
I'm a pretty competent DIYer and always try to follow the relevant IEE/IET regs.

Recently I ordered an LED bathroom cabinet from Amazon to replace an existing broken LED cabinet (the mirror was broken). The new cabinet is made out of aluminium, has LED bulbs in the glass on the front and a shaver socket fitted inside.

Before installing it, I checked for earth continuity from the CPC (it uses 3-core 1mm flex) to the metal case on the new mirror and was surprised to find there wasn't one!

This drove my curiosity as to where the CPC was terminated. On removing the top panel, I found an OEM 240v->12v LED driver and mounted directly to the metal case, the 240v+110v isolating transformer for the shaver socket. The incoming 3-core is joined to the LED driver and the transformer by the use of wire nuts, wrapped in masking tape! The CPC just feeds the 12v LED driver.

In my naive mind, the wire nuts and isolating transforming primary windings have a risk of developing a fault, e.g. a wire coming loose, which could lead to the metal case becoming live.

It seems to me the cabinet is a Class I device but it's not portable, so I'm not sure if it counts.

Of course, I could retrospectively fit a CPC, but am I right to be concerned? Should this kind of thing be reported?
 
Agree with Post #2
Some so-called double insulated light fittings etc are dubious at best, but I cannot think of a reason that a shavers socket would not require a cpc. Even though they are an isolating transformer, the core should have a cpc in case of breakdown of insulation between the windings and to the core.
 
Purchasing electrical products from Amazon is likely to be very hit and miss in terms of quality and necessary standard compliances. Some pics would help so we can form an opinion.
I grabbed this quick image, so not particularly helpful.

I agree, buying no-brand electrical stuff via Amazon was probably not a good idea.

If it was you, would you just establish an earth via a bond to the case and forget about it or return it?
IMG_2066.jpeg
 
Last edited by a moderator:
Out of interest, does it have the class II double insulated symbol on it? Not that I think it warrants one!
 
Out of interest, does it have the class II double insulated symbol on it? Not that I think it warrants one!
Nope - that's what I'd hope to find before taking it apart.

I'm guessing the use of loose wire nuts outside of an insulated enclosure means it couldn't be class II?
 

Attachments

  • IMG_2078.jpeg
    317.3 KB · Views: 46

Reply to Metal bathroom cabinet with inbuilt shaver socket not earthed in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Old two core cable in a lighting circuit with no cpc at any point All points had metal fixtures and fittings class1 At two points the live loop...
Replies
0
Views
645
Good afternoon I have recently had a bathroom makeover and had the existing shaver socket removed as I purchased a cabinet with socket enclosed...
Replies
10
Views
3K
I'm about to do wiring for a small apartment in Azerbaijan. Mostly I will try to use UK standards - ring mains with ELCBs, everywhere earthed, T&E...
Replies
10
Views
3K
I recently bought a bathroom mirror with LED & Bluetooth speakers (from Amazon). There is a double isolated symbol on the back of the mirror yet...
Replies
2
Views
1K
Hi, I live in a property built in 1911. It has had asbestos artex applied to every ceiling in the house. I am currently creating a new...
Replies
1
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock