Hi,
On site dispute needs sorting.
We have a consumer unit 3m away as in distance (not cable length) from DNO (outside meter box, flush with wall).
We currently have a 25mm 3 core SWA from DNO to consumer unit. Running within the fabric of building and it's protected from the nails and the like (SWA glanded).
Arguments are
• What is the REG (BS7671 2008 A3) for meter tails greater than 3m if any.
• Why would you need to fuse it down with a SFS if you wouldn't when you just use tails through a wall to a consumer Unit normally?
Been looking through regs book but struggling to find it in the current one.
Any help would be greatful.
 
You state the swa is glanded,if there is no switch fuse,what has been used to terminate the swa at the meter box end to convert to double insulated tails for connection to the meter

The 3 meter figure will not be found in BS7671,its a figure the supplier uses for guidance to its workers
We can use that distance as a suitable maximum for our tails to assure the supplier fuse will cover our cable for short circuit protection
 
Sorry late getting back to you didn't get any notifications.

The SWA had been useda because the consumer unit is other side of the door and there is no safe zone to run the cable, I did think about chasing it out so it was greater then 50mm or using steel plate (galvanised) to protect it though it's run but it was easier with SWA.
It's got a floating Gland which is fixed into place by cable cliets. It also has a layer of heat shrink. Which then the cable connections go straight into the DP isolator.
It hasn't got any SF because it will not fit in the meter box with the REC equipment and the client won't allow it behind as it's directly in the middle of the living room next to the door.
The "3m" rule doesn't state length only distance if I read it correct?
Any solutions would be great, and thanks for the relevant information I will look up later.
 
Recently had the same type of scenario. Both EDF and Western Power were happy for us to connect to the CU around 6m away, no problem at all!! Double checked with different people just to make sure.
 
My daughters house on a reasonably new housing estate, the CU is also 5-6 metres away from the meter. Pretty well protected on a short (3m standard) run in a cavity, but I have my doubts that the full run will meet all requirements. Meter cupboard on front wall low level to left of the front door, CU in hallway to right hand side of the door high level. Standard D/ins 25mm tails (or insulated and sheathed to keep the more pedantic amongst us happy)
 
A floating gland sounds a bit rubbish imo. I probably wouldn't of used SWA if a switch fuse couldn't be fitted. Tails and suitable protection or another box next to the meter box to house the switch fuse.
 
Wots a floating gland, I have an idea, and seen it prompted on this forum, but just to be clear.
It is where the cable is glanded off in a cavity and not to an enclosure, not something many people and myself approve of but it is common practice.
 
What is the point of a 'floating gland'? It doesn't fulfill the purpose of fitting a gland to the end of the cable.
Why not use a different method of terminating the SWA which does actually serve the purpose instead of bodgeing it?
 
[QUOTE="Nightmare1308, consumer unit is other side of the door and there is no safe zone to run the cable
Whispering mode cavity,tails ;) :)

It's got a floating Gland which is fixed into place by cable cliets. :(


It also has a layer of heat shrink. Which then the cable connections go straight into the DP isolator. :(

It hasn't got any SF because it will not fit in the meter box with the REC equipment :(

[/QUOTE]

Bit glum with this post
 
Had the same feeling when i see it installed by the team.
But it has been glanded and banjo has also taken down to the met. The SWA gland and banjo has been covered with waterproof rubber taping to protect it from water ingress if ever possible.
The Rec double pole switch is within a REC meter cupboard but trying to understand the risk of the SWA core being damaged or we just frowning apon this?
The fact it is a earthed metallic covering (SWA) does it require a safe zone and it's most likely going to be 50mm deep after the dot and dab is lined up with the stud wall.
The idea with tails in a cavity, has been pulled via the NICEIC before that's why we avoid that route as the single cables can be hit if not protected, e.g cavity wall insulation drillers.
we can only work with what we got currently but looking to see if any regulations are broken ? I
no that it don't make any of this better and it's not my work, I'm just trying to settle the debate of who's right and who's wrong with regulations.
Moving forward with we trying to come to a solution of what to do but struggling with client as neither of my solutions are liked that's why this all started.

Just to clear the floating gland up, (Short and long of it) manufacturers instructions on some telecoms kit is specified to be done that way. As much as I didn't like it originally NIC couldn't advise otherwise. But we all do different line of works within the electrical industry
 
I would consider the heat shrink not giving conductors adequate mechanical protection. The fact you could never fit the heat shrink up into the cable sufficiently would render the conductors as not being suitably enclosed. It is a poor method to solve a problem and I always comment on an EICR if I see such a situation.
 
I must be interpreting the regulations differently as I thought the meterbox was an enclosure (equipment surround by a barrier). Where is the risk of mechanical damage to the cable if the meter box was in a sound condition ?
Just trying to understand your point of view.
Is there any regulations out there for the main topic?
 
A meter box as a suitable enclosure for a cable joint (like a giant junction box), if I've understood correctly?
Plenty I see have broken doors and since householder commonly approaches the meter anyway (to take a reading) I don't think the box can be relied upon as a barrier. But that's just my thought.
 
Yes but on a condition report you would only report on the safety of the meter box at time of test, we can't retrospectively apply regs.
I'm still trying to work a way round for the lads on this issue, I don't disagree with the SF idea but it's not going to fit next to the REC and even if I removed there double pole isolator (which I can as I'm MOCOPA approved) what can I fit in the meter box.
What would you do "Wilko" with what they got?
As it's a 25mm 3 core SWA coming though the top knock out (with fire resistant foam to seal the cavity when it's done).
My biggest struggle is with the designer as he saying find me regs showing he's wrong.
Thanks for your replies.
 

Reply to Meter Tails in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Just wanted to know which people use. My case. Client converting attached garage into new rooms. Consumer Unit has to move to accomodate this...
Replies
7
Views
1K
Hi all, Customer has an extension and this compromises existing meter position, DNO is extending incomer and putting meter box on a different...
Replies
3
Views
426
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
806
On a new build site how/ why are people getting away with installing meter tails over 3metres in length and behind dot and dabbed walls with no...
Replies
7
Views
2K
Hi all, My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock