Discuss Meter Tails in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

I would consider the heat shrink not giving conductors adequate mechanical protection. The fact you could never fit the heat shrink up into the cable sufficiently would render the conductors as not being suitably enclosed. It is a poor method to solve a problem and I always comment on an EICR if I see such a situation.
 
I must be interpreting the regulations differently as I thought the meterbox was an enclosure (equipment surround by a barrier). Where is the risk of mechanical damage to the cable if the meter box was in a sound condition ?
Just trying to understand your point of view.
Is there any regulations out there for the main topic?
 
A meter box as a suitable enclosure for a cable joint (like a giant junction box), if I've understood correctly?
Plenty I see have broken doors and since householder commonly approaches the meter anyway (to take a reading) I don't think the box can be relied upon as a barrier. But that's just my thought.
 
Yes but on a condition report you would only report on the safety of the meter box at time of test, we can't retrospectively apply regs.
I'm still trying to work a way round for the lads on this issue, I don't disagree with the SF idea but it's not going to fit next to the REC and even if I removed there double pole isolator (which I can as I'm MOCOPA approved) what can I fit in the meter box.
What would you do "Wilko" with what they got?
As it's a 25mm 3 core SWA coming though the top knock out (with fire resistant foam to seal the cavity when it's done).
My biggest struggle is with the designer as he saying find me regs showing he's wrong.
Thanks for your replies.
 

Reply to Meter Tails in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Just wanted to know which people use. My case. Client converting attached garage into new rooms. Consumer Unit has to move to accomodate this...
Replies
7
Views
1K
Hi all, Customer has an extension and this compromises existing meter position, DNO is extending incomer and putting meter box on a different...
Replies
3
Views
418
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
784
On a new build site how/ why are people getting away with installing meter tails over 3metres in length and behind dot and dabbed walls with no...
Replies
7
Views
2K
Hi all, My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock