Discuss Minor Predicament over RFC Length in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1,228
Hi,

I have just started a new build today, its a large U shaped bungalow with vaulted ceilings etc.

I have split the property down into a lot of circuits to help with things due to cable runs etc.

I have just wired a section of it today, I was going to do it all in 4mm radials, but by the time I had got to the end of the section (bedroom, Wardrobe, Study & Entrance Hall) I had used 96 meters, this does not include the leg back to the board which is a further 13 meters....

I had given it though on paper, but then when I started cable routes were not quite so straight forward etc.

Anyway, my problem I have now is that the R1+R2 for that circuit at say 110 meters, will be 1.83 Ohms, which is way too much as was going to put it on a 32A, jees I would have to drop it to a 16A to comply.

So then thought, its ok, illt turn it into a ring, total length will then be 125 meters give or take a meter.

But then thats introduced another issue...

So I am thinking about VD,

Assuming 20A at the furthest point plus an additional 12A evenly distributed, the Ib of 32A then becomes (32 + 20)/2 = 26A, which I would think its fine.

4 x 11.5 x 1000 / 26 / 16 = 110 meters....

So i have got 125 meters, and to stay inside 11.5v I need it to be 110 meters.

However, the predicted readings are:

r1 = 0.57
rn = 0.57
r2 = 1.51

R1+R2 = 0.59

Should I be concerned or even bothered about the 110 meters issue or do I drop it to a 25A or 20A RCBO? but thats not going to overcome the VD.

The Zs will be well within the 1.1 Ohms for 32A

The problem is, there's no way I am going to run 6mm radials, thats just silly.

The other half of the house is even further away from the board, I have intentionally split the circuits down to minimize on length but the further circuit the other side, will be over 100m for a ring and about 80m as a radial...
 
Last edited:
Never had to deal with such long runs as that. Wouldn't one option be to run say a 10mm tail from the broad to closer to the ruing and then run the ring from the end of the 10mm tail?
You'll lose less VD over the 10mm than you would over 2 X 2.5 (you'll lose half as much in fact)
 
in your first scenario, as murdoch said, your assumed Ib is way over. i'd be inclined to assume more like 10 - 12A.

as for the second, you could run a 10mm feeder and then create a ring from that, forming a lollipop circuit.
 
in your first scenario, as murdoch said, your assumed Ib is way over. i'd be inclined to assume more like 10 - 12A.

as for the second, you could run a 10mm feeder and then create a ring from that, forming a lollipop circuit.

Even 10A seems high for those rooms..
 
I take on board what you are saying about the loadings, however, how does it work in the event that someone does pull say 2o amps? it then doesn't comply.
 
What you have to remember is the mV/A/m values are based on maximum CCC/70 degree conductor operating temp...The cable is not going to be maxed out so in reality the volt drop is going to be less than calculated as it proportional.
 
Last edited:

Reply to Minor Predicament over RFC Length in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
671
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
801
Hey there, Sorry I’ve just joined up. I’m a qualified electrician/Electrical engineer. Recently sat my 2391-52. My question is I had a fault...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock