Discuss Mis wording in guidance 3 in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Reaction score
1
Evening all

Currently studying to take my 2391 course, in guidance note book 3, page 23, 553.2.2 it says "Particular attention should be paid to the requirements for cable couplers to ensure that the connector (female part) of the couplers us fitted at the end remote from the supply."

Surely this is mis worded and should be male part! The male part should not be on the supply side and there will be 'at the end remote from the supply!'

thank you
 
It is correct, the female coupler should be the live end just like a wall socket.
If it was the male coupler the live terminals would be exposed to the touch.
Perhaps if anything, the word 'remote' should be changed to 'furthest' from the supply, as 'remote' implies it may not be connected at all.
 
Ah, it’s all in the words ...
The plug goes into the socket (near to the supply) and the female part is at the remote end (furthest from the supply). So it seams ok to me :) .
 
Ah, it’s all in the words ...
The plug goes into the socket (near to the supply) and the female part is at the remote end (furthest from the supply). So it seams ok to me :) .
It is correct, the female coupler should be the live end just like a wall socket.
If it was the male coupler the live terminals would be exposed to the touch.
Perhaps if anything, the word 'remote' should be changed to 'furthest' from the supply, as 'remote' implies it may not be connected at all.

Aha I think I've got it. The supply is the light source or plug socket supplying light or power to the user. I was incorrect in thinking of the supply as from the incoming cable into the property.

At least I bloody well hope that's it, thank you guys
 
Aha I think I've got it. The supply is the light source or plug socket supplying light or power to the user. I was incorrect in thinking of the supply as from the incoming cable into the property.

At least I bloody well hope that's it, thank you guys

You misunderstand. As with an extension lead, the plug goes to the supply, the trailing socket - female part - is at the other end, remote, from supply. You light source or appliance goes in here.
 
In the RF world typically "plug" is the cable connected part, and "socket" is the chassis fixed part, then male has the protruding pin and female the matching orifice for the pin. But often the terminology is simplified so plug is male and socket is female.

But however it is named, the critical aspect is you should not be able to touch a live conductor.
 

Reply to Mis wording in guidance 3 in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

Hi all, Probs a simple one here but when testing a 3 phase board for ze as part of a periodic inspection plus part initial verification of a...
Replies
4
Views
1K
I have a customer with a farm who has a barn containing a large 3 phase generator which powers various equiptment at that location. A single...
Replies
11
Views
1K
When I bought my house we had it inspected before buying to highlight faults, so the inspection and testing done by RICS Chartered Surveyor and...
Replies
13
Views
3K
Is there a room in professional PAT testing for a business model other than 'per unit'? I ask because I've been giving this some thought. I've...
Replies
40
Views
9K
  • Locked
Hi, we need some advice on our scenario with regards to our rewire plan. I will get this out of the way first... We are planning to put the house...
Replies
24
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock