Hi. I'm new to the board and have two questions about security lighting with motions sensors.

1) I have 2 new LED security lights and 2 new motion sensors. The instructions says to only install one sensor per switch. Both lights are on the same switch and I want a sensor on each light, one in front of the house and one in back. Is there any valid technical reason to only have one motion sensor on the same switch?

2) The lights are 100 watt LED each. So 100 watts per sensor. The sensor says 500 watts incandescent/tungsten/halogen or 50 watts LED. Again is there a valid reason why the sensor can only handle 10% of the load on LED lighting?

Thanks for you help.
 
Can't see any reason why you shouldn't connect sensors in parallel.
I would expect the sensor to be derated for LED use, because of the greater inrush (surge) of current at switch on, but 90% seems excessive.
 
Should I consider adding a relay. Let the motion sensor control the relay and the relay turn to power on?
 
If the motion sensors are purely solid-state, ie no relay inside, and you connect them in parallel, when one switches on it may prevent the other from switching on.
At least for solid state switches this is true, as apparently they need a voltage across them to operate!
 

Reply to Motion sensor instructions says one sensor per switch, Why? in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Good afternoon! I've recently wired a lighting system, where one light switch (a motion sensor) turns on two lights, but another motion sensor...
Replies
3
Views
1K
On either side of my front door is a motion sensor wall light - it looks like both lights operate from one light switch inside the house. The...
Replies
2
Views
1K
I have a baffling problem with a newly-installed PIR floodlight and I'd like advice from the forum as to whether it's defective (and should be...
Replies
5
Views
589
In my apartment block, our hallway has a mix of LED bulkhead lights (all same brand, 5 of them) some incandescent ones (x4). They are on a circuit...
Replies
0
Views
913
First, sorry if I'm not in the correxct thread. I'm trying to replace an old switch with a WIFI switch and cannot seem to do it right. There are...
Replies
1
Views
357

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock