Hi all. I'm new to this forum so thank you for having me.

I'm having an issue with my bathroom lights. I have x4 MR11 3.5mm Spots. They've been up about 8 years without ever having to change a bulb. They are operated from a 2 switch cover outside the bathroom, one for the lights and the other switch for the fan, the fan is working fine.

Not sure if this is a coincidence, I have a razor socket inside the bathroom which I used for the very first time a few days back having received an electric toothbrush. Since using it, my lights stopped working.

I have replaced all the bulbs with new LED MR11 bulbs and unfortunately they still don't work.

Ive also removed the light switch cover and razor cover the check for loose wires, everything seems fine.

My expertise is wiring a plug only hence I've arrived here.


I would appreciate any advice before I call out an electrician.

Many thanks in advance.
 
Hi all. I'm new to this forum so thank you for having me.

I'm having an issue with my bathroom lights. I have x4 MR11 3.5mm Spots. They've been up about 8 years without ever having to change a bulb. They are operated from a 2 switch cover outside the bathroom, one for the lights and the other switch for the fan, the fan is working fine.

Not sure if this is a coincidence, I have a razor socket inside the bathroom which I used for the very first time a few days back having received an electric toothbrush. Since using it, my lights stopped working.

I have replaced all the bulbs with new LED MR11 bulbs and unfortunately they still don't work.

Ive also removed the light switch cover and razor cover the check for loose wires, everything seems fine.

My expertise is wiring a plug only hence I've arrived here.


I would appreciate any advice before I call out an electrician.

Many thanks in advance.
Is the shaver socket still working ?
Are all the other lights working ?
Is anything tripped in the consumer unit ?
 
Is the shaver socket still working ?
Are all the other lights working ?
Is anything tripped in the consumer unit ?
All 4 lights are not working in the bathroom, however all the upstairs lights are working fine.
The shaver socket is still charging my toothbrush.
Nothing is tripped on the consumer unit.
Thanks for your reply much appreciated.
 
All 4 lights are not working in the bathroom, however all the upstairs lights are working fine.
The shaver socket is still charging my toothbrush.
Nothing is tripped on the consumer unit.
Thanks for your reply much appreciated.
You really need to have a meter to check supplies.
It could be anything from a failed switch or a bad joint.
It's highly unlikely to be 4 failed transformers /lamps.
 
You really need to have a meter to check supplies.
It could be anything from a failed switch or a bad joint.
It's highly unlikely to be 4 failed transformers /lamps.
I have an electrical pen the lights up when you touch inside a socket.
Would you recommend I unsrew the double light switch and touch the connected wires individualy with the pen while the swith is in the on position.
Forgive me, I'm sure there must be an official name for the tester pen.

Update - it says its non contact voltage detector. It seems to work without unscrewing the switch fitting. I turn the pen on and it flashes red on both when I touch the switches.
 
Last edited:
I have an electrical pen the lights up when you touch inside a socket.
Would you recommend I unsrew the double light switch and touch the connected wires individualy with the pen while the swith is in the on position.
Forgive me, I'm sure there must be an official name for the tester pen.

Update - it says its non contact voltage detector. It seems to work without unscrewing the switch fitting. I turn the pen on and it flashes red on both when I touch the switches.
A non contact pen isn't a very reliable way of testing, It could be that you have a loss of the neutral.
 
You need to find out if the transformer has packed up.
 
You need to find out if the transformer has packed up.
I've got a little bit further.

I've found the transformer (in picture)
The lights are on a chain of 4.
When I touch with my non contact voltage detector, the mains wire into the transformer, the output cable from the transformer, and all 4 wires going into each bulb voltage pen lights up suggesting there's power.

Do you think I still need to replace the transformer?

Many thanks in advance.
 

Attachments

  • IMG_20230710_143949.jpg
    236.7 KB · Views: 20
I've got a little bit further.

I've found the transformer (in picture)
The lights are on a chain of 4.
When I touch with my non contact voltage detector, the mains wire into the transformer, the output cable from the transformer, and all 4 wires going into each bulb voltage pen lights up suggesting there's power.

Do you think I still need to replace the transformer?

Many thanks in advance.
Reading what's written on the transformer, it seems to me likely that your new led bulbs do not add up to the minimum load that the transformer needs, namely 35watts. It's an electronic "transformer" specifically for halogen bulbs, so I think your choice is either to replace the bulbs with the halogen type, or buy a new 12V transformer suitable for driving your four LED bulbs.
But you really need a better method of testing than a volt stick, or someone to check this out for you. A multimeter would give a much better indication of what's going on, but in the meantime you could try replacing one led bulb with a halogen type and see if it all springs back to life!
The fact that your pen tester lights up on the wires going to the bulbs (from the SELV transformer) does possibly suggest a lost neutral to the supply? as has been mentioned before.
 
Last edited:
Reading what's written on the transformer, it seems to me likely that your new led bulbs do not add up to the minimum load that the transformer needs, namely 35watts. It's an electronic "transformer" specifically for halogen bulbs, so I think your choice is either to replace the bulbs with the halogen type, or buy a new 12V transformer suitable for driving your four LED bulbs.
But you really need a better method of testing than a volt stick, or someone to check this out for you. A multimeter would give a much better indication of what's going on, but in the meantime you could try replacing one led bulb with a halogen type and see if it all springs back to life!
The fact that your pen tester lights up on the wires going to the bulbs (from the SELV transformer) does possibly suggest a lost neutral to the supply? as has been mentioned before.
I've now ordered a new transformer suitable for LEDs and some halogen bulbs just to test on the current transformer. They arrive tomorrow.

'Lost neutral' sounds interesting, but much beyond my minimal knowledge which amounts to wiring a plug and maybe a light fitting change.

I'll try the new halogen bulbs first, if no success, I'll swap the transformer to the new LED one using the LED bulbs.

If that doesn't work, like you say it's probably a lost neutral. In that situation I'll have to call in a professional.

I'm bit frustrated as I've taken the floating ceiling down and I didn't want this to beat me lol

I'll update on here tomorrow.

Thanks for your detailed reply. Very much appreciated.
 
It's just jargon meaning the blue (or black if old wiring!) neutral wire has become disconnected somewhere on its way from the supply to the transformer in the ceiling 🙂
Wohooo they're working.

As I said in my previous post, I tried the new halogen bulbs first, unfortunately that didn't work.

Then I changed the transformer form the halogen transformer to the new LED supported transformer, then fitted the new LED MR11 bulbs and thankfully they worked.

I guess we can conclude that the halogen transformer was defective.

Now I've got the job of putting my floating ceiling back together, a job I learned I didn't need to do, as seen in the picture, it turns out the transformer was hidden above a hole in the original ceiling plasterboard between the loft insulation, I should have lifted that up when I first got in the loft. It's a bit of a chore putting it all back, but I'll do it with the biggest smile on my face.

Thanks to everybody who responded, I could not have done it without your help, I bow to your expertise.
I've leaned a few things, didn't know about transformers and the different types. It was a bit daunting, but it goes to show, you can achieve anything with a bit of patience, confidence and some good advice.

Thanks again very much appreciated.

David 😊👍💡
 

Attachments

  • IMG_20230711_165808_edit_52298913770664.jpg
    288.4 KB · Views: 15
Before you put it all back together, there are covers missing off of that driver, and it is a requirement that the grey sheath of the mains cable enters under that cover, with none of the brown or blue wires outside of it.
As it is, it merits a C2 "unsatisfactory", or even a C1 "unsatisfactory", depending on how exposed the live terminals are, if discovered by someone carrying out an EICR on the property.
 
Before you put it all back together, there are covers missing off of that driver, and it is a requirement that the grey sheath of the mains cable enters under that cover, with none of the brown or blue wires outside of it.
As it is, it merits a C2 "unsatisfactory", or even a C1 "unsatisfactory", depending on how exposed the live terminals are, if discovered by someone carrying out an EICR on the property.
Hi,

I put the ceiling back together and it wasn't until then when I realised I had not put said covers back on the exposed wires you mention, I found the covers on my bed with the screws later. Luckly, I now know I can access my new transformer from the loft through the hole in the original ceiling. I intend to put them back on tomorrow on my day off, I'm worried it may cause a fire being near the loft insulation.

Many thanks for pointing that out and well spotted.

David 😊👍
 

Reply to MR11 3.5mm Spots stopped working in the Lighting Forum area at ElectriciansForums.net

Similar Threads

I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K
My bedroom light stopped working. The ceiling rose looks fine. No other lights are affected in the property and the fuses have not tripped. The...
Replies
18
Views
1K
My kitchen has track lighting. It consists of three halogen light bulbs. I've had the fixture for more than 25 years with no issues. Last night...
Replies
10
Views
937
Hello, I've installed a Monsoon Extractor Fan kit today, all is up and running and everything is working with the exception of the LED. When I...
Replies
0
Views
721
  • Locked
I've wired up my spots however the main light [the one that was once a ceiling rose] works as intended with the light switch, but the rest are...
Replies
2
Views
594

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock