Discuss My ceiling light's not working in the UK Electrical Forum area at ElectriciansForums.net

Mischief

DIY
Reaction score
1
I wanted to remove a cut off pull cord attached to the ceiling so I turned the electrics off, disconnected the wires and wrapped each one in insulation tape. Then I pushed them up into the ceiling. Oops. Now my bedroom ceiling light won't work. They must be connected. My question is, can I make the ceiling light work without reconnecting the pull cord as I've now filled and painted over the area? I'm not an electrician (you probably realise that).
 
i assume it's 2 way switching.in which case toneed to connect 2 of the wires that were in the pullswitch. common and L1 as was. or rejig the wall switch. post a pic of the wall switch (poweroff and switch faceplate off) so i can see the connections.
 
What you have done is dangerous.
there are live wires floating around in the roof space that have only a bit of sticky tape preventing contact with things like water, insulation, etc.
it can be fixed, it requires a proper junction box and someone with the skills to identify the correct cables to join together and keep separate.
half hour job for a professional, get someone in and have it done correctly.
 
Photo as requested.
 

Attachments

  • 16184723265042379806168375669995.jpg
    228.9 KB · Views: 20
how many cables wer in the pull switch?
 
Could those cables be any more twisted?

looks simple enough, but as tel says, what was at the pullcord? Hopefully other end of the 3 core... (red,yellow, blue)

don’t remove anything until instructed. And I hope you’ve got the power off.
 
needs some re-jigging to convert to 1 way switching.. IMO, beyond the scope of DIY. MF box at pulllswitch position might be required.
 
cost about £60 for as spark to sort that out. what price safety.
 
Red, yello, blue and green sleeved?

I’m wary of suggesting what needs to be done at the wall switch, as it’s not in great condition as it is.
To my eyes, the red at the pullswitch was /is still a live feed cable.
leave the power off just now, if you just taped up the ends.

Any members in N. Yorkshire need a quick job?
 
I’m sorry to be blunt, but if you want to see another birthday, don’t mess with electrics.

taping up the ends of a cable doesn’t fill us with confidence that you know what you’re doing.

the forum rules don’t allow us to give you a step by step instructions, although my guess is it’s a 5 minute job... however, without testing beforehand, my guess is just that.... a guess.
 
I’m sorry to be blunt, but if you want to see another birthday, don’t mess with electrics.

taping up the ends of a cable doesn’t fill us with confidence that you know what you’re doing.

the forum rules don’t allow us to give you a step by step instructions, although my guess is it’s a 5 minute job... however, without testing beforehand, my guess is just that.... a guess.
Wonderful. My daughters tell me this all the time ? Better stick to what I CAN do in future.
 

Reply to My ceiling light's not working in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, have an old bathroom fan. Which has two wires the black and red (line and neutral). The fan has no isolator switch and was powered when the...
Replies
3
Views
658
Hi all. Removed an ancient light fitting, replaced with a newer one, the light comes on but can't be turned off with the switch. It was working...
Replies
23
Views
702
I live in a warehouse condo, converted about 20 years ago. The building dates to about 1870 but with the conversion, all of the electrical was...
Replies
3
Views
492
I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
452
My ceiling fan does not have light. couple of weeks the light started blinking then it went off. I did my search and everyone says that I need to...
Replies
1
Views
909

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock