Discuss My Heatrae Sadia Electrolux is not heating water at night - help! in the UK Electrical Forum area at ElectriciansForums.net

K

Kelly Thompson

My central heating is working fine and if I demand water, then I get a small supply of hot water within an hour. The problem is my water does not heat up over night on the peak rate as it should do, so I do not have hot water unless I use the demand button. There is no alarm sign and all seems to be working fine apart from this. The pressure is at 1.5-2 (I recently reset the pressure, hoping this may help). Can anybody suggest what the problem may be?
 
Google doesn't recognise "Heatrae Sadia Electrolux", but there is a range of Heatrae Sadia Electromax boilers, which I suspect this is. They are an electric boiler, combined with a fairly conventional hot water cylinder, which has an immersion heater at the bottom and a boost immersion heater part way up.
If the water isn't heating up overnight, then either the off peak supply is not reaching the lower immersion heater, or the immersion heater is faulty. First job is to test to determine which.
The immersion heater contains a thermostat to set the hot water temperature, and a second thermostat set at 90 or so degrees, which acts as a safety cut out, if the first thermostat fails on. The second thermostat is resettable by a small button, and may be the immediate problem, but that then raises the question as to why it tripped.
 
Heatrae Sadia Electromax has 3 (count them) supplies, 2 for immersion heaters top (boost) and bottom (off peak), 1 for central heating side. any of the circuit breakers tripped ? and of course the thermostats have got thermal cutouts with reset buttons under the cover always worth checking with all the power off first
 
I have the exact problem. Central heating working fine but water does not heat up over the night. Pressure is fine too. Have you resolved your problem and may I know why ? That could help a lot. Many thanks!
 
I have the exact problem. Central heating working fine but water does not heat up over the night. Pressure is fine too. Have you resolved your problem and may I know why ? That could help a lot. Many thanks!
If it only normally heats overnight, then you either have an off peak circuit supply to the lower immersion heater or an external timer (faulty timers can often be the cause). Have an electrician check that supply from consumer unit, should be on a 16A breaker to immersion heater and also check if the thermostat reset button needs to be reset. If it's the reset button it might work fine after that, if it trips again the thermostat is allowing the tank to overheat and needs to be replaced. IF there is power to the immersion heater and the thermostat has not tripped or has no reset button, then one or the other is faulty, an electrician can quickly establish if it's the thermostat and it's a fairly simple repair, the heater itself is a bigger job and needs the tank drained to replace the heater
 
The reset button on many immersion heaters lies between two live terminals when the power is on, so make doubly sure that the power is off.
I have had more than one customer of mine find out this the hard way.
 
Central heating works off an Amptec c600 boiler which is totally independent to the hot water. My advice without looking but after many years of working with these units is it is most definitely the stat has burnt out. If you press the boost button on the front do you get hot water after about 1 hour?
 
Central heating works off an Amptec c600 boiler which is totally independent to the hot water. My advice without looking but after many years of working with these units is it is most definitely the stat has burnt out. If you press the boost button on the front do you get hot water after about 1 hour?
Yes, last time it took around 45mins and had hot water only for couple minutes.
 
Yes, last time it took around 45mins and had hot water only for couple minutes.
The boost only operates the top immersion heater, but it clearly works, it would take a few hours to heat up a tank from cold, your issue is the bottom immersion heater, and it needs to be checked as stated above, it's a simple test and should identify if it's the thermostat or heater in minutes
 

Reply to My Heatrae Sadia Electrolux is not heating water at night - help! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I'm in a bit of a pickle trying to set up my hot water and central heating systems. Got a gas boiler with a pressure tank and a motor...
Replies
7
Views
847
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
I have a Firebird oil boiler that is controlled by a Honeywell timer (no thermostat) that has channels for hot water and central heating...
Replies
8
Views
436
I get the feeling asking this will produce head shaking, I'll ask anyway... I have a hot water tank with a single immersion heater. Currently...
Replies
7
Views
1K
Good afternoon chaps, I have an Alpha E-Tec 33 combi boiler (with Google Nest 3rd Gen thermostat) that occasionally fails to put out hot water...
Replies
10
Views
952

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock