Hi all , after some opinions on N-E fault or ring main.

After chasing this fault and ruining my bank holiday weekend , ring main IR readings as follows

L-E >999
L-N>999
N-E>0.98Mohm

I have narrowed it down to a cable spurred from ring main , astonishingly the 3no. Cables in the twin switched socket all individually test out at >999 across all conductors. It’s only when connected together that it causes the low reading , like there is a low resistance between 2 different cables ,any ideas?

TNCS supply , split load consumer unit
 
Try a wander lead from the MET to each of the 3 conductors at end of the spur, with the spur disconnected at the branch point.
It could be a damaged cable touching a pipe that is bonded.

Also check end-to-end ring integrity as a broken ring can upset otherwise sound logic!
Finally double check that when the spur is disconnected at the branch point and the other two cables wago'd together, there is no fault showing up back at the board.
 
Last edited:

Reply to N-E fault bank holiday ruined in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
497
Hi all, After some options/opinions on fault finding N/E fault on ring final as fairly newish to being out alone. Customer wants to upgrade from...
Replies
7
Views
1K
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
498
A silly fault in a circuit only 4m long is currently eluding me! This is ECIR remedials of a landlords supply in a block of flats. Circuit 2 =...
Replies
3
Views
891
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
684

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock