Discuss need a capacitor across relay contacts to arrest arcing. wondering about type and value ? in the UK Electrical Forum area at ElectriciansForums.net

You will get an arc when you make or especially when you break a 7 Amp load, this is normal and usually with an AC supply it will only last for a half cycle which is a few miliseconds. The relay contacts should be designed to handle the arc if the relay is sized correctly and there's no need to retrofit any components to mitigate the arc.
 
You will get an arc when you make or especially when you break a 7 Amp load, this is normal and usually with an AC supply it will only last for a half cycle which is a few miliseconds. The relay contacts should be designed to handle the arc if the relay is sized correctly and there's no need to retrofit any components to mitigate the arc.
thanks marvo- luv the icon btw says it all-- as for the relay its an RS 356-758 and rated at 10amps but seeings as the load i am running is resistive and not inductive the spark looked rather excessive and i would have liked to get rid of as much as possible to prolong the life of the thing.. harry
 
For suppressing 230V AC contacts, 0.1μF is typical. It's good to add a series resistor of a few hundred ohms to prevent contact welding if the capacitor is still charged when the contacts close. The ideal values depend on the inductance of the load and the permissible leakage current that will flow through the capacitive reactance into the load while the relay contacts are open. A common solution is to use a commercially made snubber network combining R & C in one unit.

See:
RC snubber networks from RS Components
 
For suppressing 230V AC contacts, 0.1μF is typical. It's good to add a series resistor of a few hundred ohms to prevent contact welding if the capacitor is still charged when the contacts close. The ideal values depend on the inductance of the load and the permissible leakage current that will flow through the capacitive reactance into the load while the relay contacts are open. A common solution is to use a commercially made snubber network combining R & C in one unit.

See:
RC snubber networks from RS Components
thanks for that- i have probably got numerous parts somewhere tucked away in my workshop. i would have thought that the value may have been slightly different. btw i am supplying a print bed heater for a 3D printer (hence resistive load) so when the 7 amp heater switches out the arcing can be considerable and i didn't want to knacker the contacts too soon as it switches at quite a rate.
 
If such a load is being switched on an off a lot such as to closely maintain a temperature, it is common now to find solid state relays used for this purpose. Be aware though there will need to be some sort of thermal protection fitted to the heater as solid state relays can fail permanently on.
 
If such a load is being switched on an off a lot such as to closely maintain a temperature, it is common now to find solid state relays used for this purpose. Be aware though there will need to be some sort of thermal protection fitted to the heater as solid state relays can fail permanently on.
Hi Freddo. yes that's one reason why electronic relays don't really figure at such high currents plus having to add other protections and making things more overly complicated than they need to be- i find my self already having to build a box of tricks for this project and one can go on and on and what was a simple project can become cumbersome. and as my mother used to say > the more there is the more you've got to go wrong :) thanks anyway. harry
 
Solid state relays should be more reliable than mechanical relays and are available with contact ratings over 100A. Most are 0V switching which reduces switching interference. I spent a few weeks a while back helping a local manufacturer build control panels for milk pasteurisation equipment, the design used a small solid state relay to switch a 3KW immersion element.
 
If such a load is being switched on an off a lot such as to closely maintain a temperature, it is common now to find solid state relays used for this purpose. Be aware though there will need to be some sort of thermal protection fitted to the heater as solid state relays can fail permanently on.
Hi Freddo. yes that's one reason why electronic relays don't really figure at such high currents plus having to add other protections and making things more overly complicated than they need to be- i find my self already having to build a box of tricks for this project and one can go on and on and what was a simple project can become cumbersome. and as my mother used to say > the more there is the more you've got to go wrong :) thanks anyway
Solid state relays should be more reliable than mechanical relays and are available with contact ratings over 100A. Most are 0V switching which reduces switching interference. I spent a few weeks a while back helping a local manufacturer build control panels for milk pasteurisation equipment, the design used a small solid state relay to switch a 3KW immersion element.
hi. i was saying to someone last night about hearing the click of a mechanical relay is quite satisfying. however i take your point about being able to switch hefty loads with electronic relays.
 

Reply to need a capacitor across relay contacts to arrest arcing. wondering about type and value ? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

A friend of mine asked me to look at here PV system as she is not getting any power (and thus money) from it. First real issue is the Aurora...
Replies
8
Views
5K
As a retired electrician, I need to specify a new type B board for a village church. Principal load is heating. Ipfc phase to phase is 1.1kA...
Replies
10
Views
1K
Hi everyone Recently I have come across an advert of someone selling Afdds C type and the person mentioned the need to sell because Zs was too...
Replies
16
Views
3K
Hi friendly people, As you may be aware, I'm a plumber, so quite possibly what I am seeing is correct, though it seems a bit odd to my untrained...
Replies
4
Views
5K
I quite often contribute on other's posts about issues with RCD's, thought I'd tell you about what happened to me yesterday as a little bit of a...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock