Whilst i can only recommend i just think a new consumer unit would enhance the safety of the installation. It would be more accessible, provide extra ways for circuits that are doubled up. There seems to be quite a few sockets that are spured of an already unfused spur from the ring. I was going to suggest splitting the ring into two radials, but again there is no room in the current unit. If im classing the boiler supply as a C2 and the customer wants a report that is satisfactory i really cant see how i am going to go about replacing the MCB for one of a lower rating