Search the forum,

Discuss New Build IR Testing RFC, can't find the issue in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
I am currently testing a 2 bed flat, all other circuits read clear. Flat Ring not so much.

Using a Megger MFT1721

L - E Reading 300Mohms but slowly
L - N Reading 400 Mohms but slowly
N -E Reading 200Mohms but slowly

Have tried breaking the ring and narrowing down the problem but both sides come up with higher readings.

Have replaced half the ring and still no change.
Each leg reads +999
You pit a couple of sockets together it starts to drop. Tried replacing parts of ring with 2.5 to see if I can clear it but its not working.

Trying replacing a lag at a time tomorrow...

The plot is a new build so I would expect the readings to jump above 300 right away, so slow readings mean I'm having to investigate.

Does anyone here have any idea what could be causing these readings?
 
I am currently testing a 2 bed flat, all other circuits read clear. Flat Ring not so much.

Using a Megger MFT1721

L - E Reading 300Mohms but slowly
L - N Reading 400 Mohms but slowly
N -E Reading 200Mohms but slowly

Have tried breaking the ring and narrowing down the problem but both sides come up with higher readings.

Have replaced half the ring and still no change.
Each leg reads +999
You pit a couple of sockets together it starts to drop. Tried replacing parts of ring with 2.5 to see if I can clear it but its not working.

Trying replacing a lag at a time tomorrow...

The plot is a new build so I would expect the readings to jump above 300 right away, so slow readings mean I'm having to investigate.

Does anyone here have any idea what could be causing these readings?
Damp
 
I am currently testing a 2 bed flat, all other circuits read clear. Flat Ring not so much.

Using a Megger MFT1721

L - E Reading 300Mohms but slowly
L - N Reading 400 Mohms but slowly
N -E Reading 200Mohms but slowly

Have tried breaking the ring and narrowing down the problem but both sides come up with higher readings.

Have replaced half the ring and still no change.
Each leg reads +999
You pit a couple of sockets together it starts to drop. Tried replacing parts of ring with 2.5 to see if I can clear it but its not working.

Trying replacing a lag at a time tomorrow...

The plot is a new build so I would expect the readings to jump above 300 right away, so slow readings mean I'm having to investigate.

Does anyone here have any idea what could be causing these readings?
Not sure I understand "replaced part of Ring with 2.5??"
 
I am currently testing a 2 bed flat, all other circuits read clear. Flat Ring not so much.

Using a Megger MFT1721

L - E Reading 300Mohms but slowly
L - N Reading 400 Mohms but slowly
N -E Reading 200Mohms but slowly

Have tried breaking the ring and narrowing down the problem but both sides come up with higher readings.

Have replaced half the ring and still no change.
Each leg reads +999
You pit a couple of sockets together it starts to drop. Tried replacing parts of ring with 2.5 to see if I can clear it but its not working.

Trying replacing a lag at a time tomorrow...

The plot is a new build so I would expect the readings to jump above 300 right away, so slow readings mean I'm having to investigate.

Does anyone here have any idea what could be causing these readings?
So let me get this straight in my head, you have taken all the accessories off the RFC? IR tested each leg of the RFC? all >999Mohm, put the accessories back on, screwed them back and the IR readings slowly rise to around 300Mohm? if thats the case then a pound to a pinch of the brown stuff it's damp walls, a new build you said?
 
So let me get this straight in my head, you have taken all the accessories off the RFC? IR tested each leg of the RFC? all >999Mohm, put the accessories back on, screwed them back and the IR readings slowly rise to around 300Mohm? if thats the case then a pound to a pinch of the brown stuff it's damp walls, a new build you said?

Yep. New build.
 
Not too sure I'd be happy with that on a rewire or new install, damp from plaster or not.
Surely this comes from the experience of un-doing all the sockets , letting them breath , getting a much better reading .. logic .
( if worried about tracking damage - I can see AFDs turning up sooner)
Is this "Damp from New Build plaster" effect common only in hot weather ?
 
any rate, my megger BM80 goes up to 100Gig on the 500V range, so ner,ner. :D:D:D.
 

Reply to New Build IR Testing RFC, can't find the issue in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
701
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
527
Recently changed a CU for a friend and today when visiting one of the RFC's RCBOs tripped. It was due attention anyway as open ring and no time to...
Replies
13
Views
1K
Hello, I’ve got an issue driving me crazy and can’t get anyone to figure it out as it’s not their issue. We had a new extension, single rear...
Replies
9
Views
1K
So I’m an apprentice and I’m just trying to get a better understanding of the science behind this because the electricians who have said it have...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top