- Reaction score
- 25,516
That is the problem with the higher rated Memshield 1 stuff a 63A second hand breaker could be £50-60.
Discuss New DB (additional) in the Commercial Electrical Advice area at ElectriciansForums.net
I'll have a more thorough look at the board tomorrow and see exactly what it is I'm working with and let you all knowThat is the problem with the higher rated Memshield 1 stuff a 63A second hand breaker could be £50-60.
Should get away with 10mm SWA for CCC, but was going to install 16mm just to keep the Zsdb as low as possible. Run will be around 8m for SWA from the upstream DB, and then the 2 circuits are RFCs ran in 4mm (again, to keep that Zs down).
If there is a problem with the Zs of the existing submain then that needs to be sorted out rather than oversizing new cables to try and achieve compliance.
Reply to New DB (additional) in the Commercial Electrical Advice area at ElectriciansForums.net
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.