Discuss new supply been put today to new building ,NO EARTH in the UK Electrical Forum area at ElectriciansForums.net

When you say no earth what do you mean?,no provision of earth from cutout, Some suppliers do not provide earth from cut out, if that is the case when meter fitted etc, they should break out the NE terminal (pme) ready for you to connect into cutout,they should also leave the stated nominal voltage plus ze of the supply.
 
When you say no earth what do you mean?,no provision of earth from cutout, Some suppliers do not provide earth from cut out, if that is the case when meter fitted etc, they should break out the NE terminal (pme) ready for you to connect into cutout,they should also leave the stated nominal voltage plus ze of the supply.

they won't provide a Ze if they ain't supplying a earth.
 
Are you out in the sticks or in a built up area .... maybe your lack of experience just means you don't recognise the service head provided may have a N/E combined block but you dont have access to it... can you post a pic if possible?

If you have never seen a TT then i can assume your experience is limited ...well we all start somewhere ;)
 

Reply to new supply been put today to new building ,NO EARTH in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, So my factory needs more power, currently 100A/3p (70KVA) => 400A/3p (200KVA) UKPN wont upgrade existing supply and are insisting on new...
Replies
1
Views
395
Morning all, Really hoping to get some advice / confirm what a few of us are thinking about a job in the future. Back ground - We have to swap...
Replies
15
Views
445
We are refurbishing an empty commercial building at the minute and I don't do commercial stuff day in day out so not entirely clued up on...
Replies
11
Views
1K
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
So far I have never had to deal with a new supply but a possible site we are looking at will need some major changes and so I wondered if folks...
Replies
2
Views
725

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock