Hi All,

absolutely aware of my own limitations as a diy' er and limit myself to replacing fittings rather than new installations.

Replaced 4 x 240v GU10 downlighters in the bathroom(ceiling 3m high) and when I turn the light switch on , the MCB trips all lights in the flat. before I replaced the fittings, I never had an issue.

1 gang light switch feeds a 1mm cable up to the ceiling and lights are connected in series, used new cable, connecting all the lives together, all the nuetrals together and earths together.

Have I missed something?
 
A very common and dangerous mistake, my money is on one of those neutrals being a switch live, if this is within your limit as you say do your have the correct equipment to test for this?
Also a bathroom is a special location.
 
Last edited:
You'll just have to double check each connection and if that doesn't find a problem, employ an electrician with suitable fault finding equipment.

Are you central Edinburgh? kind of out of my way but nice drive up the coast
 
Could you drop the lights and take some pictures? It may help to identify anything you may have missed. When you say the "...MCB trips..." do you mean the MCB or RCD, you do have RCD protection?
 
Classic lighting error, as above one of the blues must have been missing a brown sleeve as it's a switched live. Are the lights on when the switch is off?
Do you have the before and after photos of the wiring?
 

Reply to Newby DIYer, replacement light fittings trip the MCB in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Hi all. Removed an ancient light fitting, replaced with a newer one, the light comes on but can't be turned off with the switch. It was working...
Replies
23
Views
833
I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K
I'm not sure what's going on with my kitchen light. I've replaced an old 28W CFL fitting with a new 4 x LED GU10 fitting (a cheap one from...
Replies
11
Views
1K
Hi, does anyone know where I can buy a replacement light fitting like the one in the picture? It takes a s15 bulb 284mm and the length can be no...
Replies
1
Views
818
I have a strip light in the kitchen operated from a single switch. I want to replace it with a straight bar 4 spot array. There are three supply...
Replies
2
Views
488

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock