Iona222

Trainee
Reaction score
41
Not getting a continuity reading on the cooker circuit. I'm doing I.r. test and its low between l. N. Any ideas what the issue could be.

The cooker sockets is working also.
 
Neon on switch between L and N?
also, what continuity test are you doing?
 
What reading are you getting. You will only get a line to cpc reading if you have connected a link across them.
 
Not getting a continuity reading on the cooker circuit. I'm doing I.r. test and its low between l. N. Any ideas what the issue could be.

The cooker sockets is working also.
What exactly do you mean by not getting a continuity reading? how low was the IR Test? cooker sockets is working also?
 
Dont want batter you with too many questions but as above can you clarify. Insulation resistance test at 500v or continuity test.
 
I have mate. I'm not getting a reading. When I link line and neutral I get 0.10 ohms

So there must be a break in either the live or the earth. Now, along with the line-to-neutral being OK, you say the socket is working so those may be a clue.

I bet Zs is poor. Although obviously dead tests should be sorted first.
 
Last edited:
This is a matter of deduction, three conductors and two linked are fine but the third when linked is not so what does this tell you.
 

Reply to No continuity on cooker circuit. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
428
A friend's partner has an interesting fault, if it is a fault. She sets the shut down timer on the cooker and when the timer goes off (which in...
Replies
9
Views
843
Hello All. I'm quite new to this game and gaining experience, but going well in the main. My customer wants to feed a Hob ( on island in centre...
Replies
5
Views
260
Hi All, We have an old Country villa in Spain. The housing electrics were not good so the house recently has been completely re-wired to a good...
Replies
2
Views
845
I'm looking at a vending hot drinks machine 2.9kW that has a thermostatically controlled hot water tank permanently attached to a water supply...
Replies
2
Views
237

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock