Discuss No earth in lights in the Canada area at ElectriciansForums.net

K

KFORDHUNTER

This might be the thickest question ever but if a lighting circuit in a house has no earth you have to add one in don't you, or is there some way around it now with say class 2 fittings and plastic switches.:eek:
 
If you go on the niceic website download section there is a download titled changing a consumer unit in a property with no earth on lights that deels with this in detail,hope this helps.
 
You can add to the aforementioned circuit but you have to make sure your part of the installion complies, ie if there is no cpc existing you can pick one up from a local circuit (same board) but it has to be 4mm. If it needs an rcd then youi have to add one. Having complied to the above you don't need to use class 2 fittings etc. Think I'm right in all that? Syure someone will correct me if I'm not>
Big Al
 
Hi,

This is my first reply, so I hope I am right in what say!! If not then I will be learning yet again!:confused:

If there is no cpc in the lighting circuit then protect by an RCD/RCBO. Change fittings and switch plates out for plastic and issue a method statement on changing a failed lamp element, i.e. non conducting step ladders etc. This is off course if there isn't the facility to retrospectively add a cpc.
 
personally i was of the opinion that a rcd detects an imbalance between ph &n usually caused by an earth fault .the o in rcbo is for overload .
is this one of those threads that tries to trip people up?
 
Spot on Wayne.

A RCD detects an imbalance between phase and neutral and will "trip out" at an imbalance more than 50% of its rating (ie a 30 mA device will trip out between 16 and 30mA). This imbalance is generally as a result of an earth fault however it does not require a cpc to function (check out wiring in some parts of Europe where no cpcs are installed but RCD incomers are used).

A RCBO meets the characteristic requirements of an RCD however also incorporates the functions of a mcb having short circuit and overload protection capabilities.
 
the head boy will be along to fill you in shortly
as tony says you need an earth path ,even if its through you! and not a cpc
 

Reply to No earth in lights in the Canada area at ElectriciansForums.net

Similar Threads

I have had these lights installed by a contractor whose work is normally very good. He has not connected the earth in each fitting as there is a...
Replies
37
Views
2K
Hi, Just interested in learning what others do when faced with an old lighting installation where there is no earth and you’re installing a metal...
Replies
7
Views
2K
I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
477
Hi, Heavy industrial spark here, never do house bashing hence the question. I currently have a light switch at the front door not doing anything...
Replies
1
Views
455
I have a strip light in the kitchen operated from a single switch. I want to replace it with a straight bar 4 spot array. There are three supply...
Replies
2
Views
454

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock