Search the forum,

Discuss Rcbo keeps tripping in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hi just wondering if someone can help me.
I have an rcbo that keeps tripping but only when the fly earth and neutral lead on the bars it trips out.
Has this happened to anyone else.
I could just replace the rcbo as this could be faulty but don't want to do that if there could be another explanation.
Cheers in advance
 
Hi just wondering if someone can help me.
I have an rcbo that keeps tripping but only when the fly earth and neutral lead on the bars it trips out.
Has this happened to anyone else.
I could just replace the rcbo as this could be faulty but don't want to do that if there could be another explanation.
Cheers in advance

Am I reading this correctly in that you've energised the circuit with neutral and earth flyleads disconnected?
 
As with any circuit.... you don't take the neutral out and energise the circuit.... you've then got 230v looking for a return path....



Are you connecting it to the correct neutral bar? All depends on the type of board is gone in to... is this an old split board being added to? ...

photos are good.
So all the power is in and when I put the fly lead earth and neutral lead in it trips
 

Attachments

  • IMG20240504150813.jpg
    346.1 KB · Views: 27
Can we see the rest of the board?

It looks to me like the board has been altered somewhat… ie so these first two slots are direct from mainswitch, the rest are through the rcd to the left….

Which means the neutral bar should be split…
 
well the OP has disappeared, never mind, a shame really, it would have been nice to see this thread to the end.
 
So all the power is in and when I put the fly lead earth and neutral lead in it trips
well then, must be a fault on the circuit, a faulty appliance if a power circuit or a faulty RCBO.
 

Reply to Rcbo keeps tripping in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Just wondering if someone could help provide an explanation as to why this might be the case when testing an RCBO. Testing the RCBO at the DB...
Replies
7
Views
311
I have an issue with a home lighting circuit 6A RCBO provides power to 13 bulbs which randomly keeps tripping, when I say randomly it keeps...
Replies
8
Views
3K
Hi all, Wondering if you could offer some advice please. I carried out a small outdoor lighting project today at a commercial property. 4 lights...
Replies
5
Views
974
I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
623
Hi, Just been scratching my head about this one and wonder if I've missed anything. A few weeks ago I installed a new circuit for a 3kw oven and...
Replies
6
Views
858

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock