petedel

Hi all, a friend of mine asked me to have a quick look at her electrics as she had been told by the gas engineer that there was no evidence of protective bonding at the gas meter.

I looked in the cupboard to find a met with only two cables attached, one green/yellow and one just green, the house had two consumer units both with six breakers in and these cables run to each of the cu's.

I cant see any bonding to gas or water, on a side note there doesn't even appear to be a stop tap on the water as when her boiler was changed they had to shut the supply of in the street.

Spoke to british gas who confirmed supply as PME and quoted £40 to come out and attach earth conductor.


Am I able to just open up the neutral link and connect a cable from here to met, or does the fact that fuse is sealed prevent me from being allowed to remove and isolate. then add bonding
 
no ive not checked the incomers but would have assumed would still need bonding due to metal pipework being an extrenuous conductive part (I know ive spelt it wrong). the main concern is the lack of an earthing conductor
 
First things first, ....Are you a qualified electrician or a so-called DI?? If you're not then i suggest you're friend employ a qualified electrian to sort this situation out.


You do ''NOT'' go making you're own earthing connections to a DNO's supply cut out!!
 
Tell her she has been caught out by a British Gas CHURNER remember BG is owned by a private equaty company who is sales driven so this happens every day where some poor old biddy gets told she could be dead because the gas pipe is not bonded I was called to one where the pipe was bonded as the pipe entered the building in the garage 1 metre away from the meter.

My advise is tell BG you want it in writing plus that you will bill them if they get it wrong or you have found they have deceived you one example being one of my customers was told that they could not support his boiler for parts as it was more than 10 years old. I told him that all boiler manufacturers must guarantee parts for 10 years after the manufacture of the boiler has ceased. So when the BG salesman called and prompted by me he asked if the service guy was on a commission plus he would expect them to confirm in writing that they no longer had parts for his boiler.

After 2 days they said well Emmm yep the service guy was on a commission and surprise surprise it looks like we can get parts for your boiler and they still have not put this in writing . This from a company who warns you that your calls will be recorded for "Training Purposes"
 
no ive not checked the incomers but would have assumed would still need bonding due to metal pipework being an extrenuous conductive part (I know ive spelt it wrong). the main concern is the lack of an earthing conductor


i'd be bonding the internal pipes anyway - if they're run anywhere near electrical services you have to provide fault protection. but if it can be confirmed that the incoming pipe is plastic, then it's not going to introduce a potential. try testing the resistance between the pipe and the MET - this should tell you if it's extraneous (although you would have to allow for supplementary bonding etc.).
 
Hi all, a friend of mine asked me to have a quick look at her electrics as she had been told by the gas engineer that there was no evidence of protective bonding at the gas meter.

I looked in the cupboard to find a met with only two cables attached, one green/yellow and one just green, the house had two consumer units both with six breakers in and these cables run to each of the cu's.

I cant see any bonding to gas or water, on a side note there doesn't even appear to be a stop tap on the water as when her boiler was changed they had to shut the supply of in the street.

Spoke to british gas who confirmed supply as PME and quoted £40 to come out and attach earth conductor.


Am I able to just open up the neutral link and connect a cable from here to met, or does the fact that fuse is sealed prevent me from being allowed to remove and isolate. then add bonding

Please tell you are NOT going to do this??

By the sound of your posts you clearly don't understand equipotential bonding.
 
Please tell you are NOT going to do this??

By the sound of your posts you clearly don't understand equipotential bonding.

What's the betting he will,.... and probably already has!! lol!!

He hasn't been back since confirming (as he thinks) it's a PME connection!!
 
54, no ive not made any connections. just offered what help I could by visual inspection. Shagbite, no I don't 100% trust british gas and now agree that they should come and do the connection, that way no one can point the finger if its not pme
 
how common is it to find no earthing conductor in old terrace houses? im unsure how old the installation is and there are no labels at all on either of the cu's and both have wylex push in breakers there was a reading of I think 0.71 ohms from the met to the gas meter which is approx 4 metres away
 
Not sure what's missing here. Are BG coming to fit an earthing conductor or main protective bonding?
If it is an earthing conductor and it is PME I would think that is their responsibility free of charge!!
 
Last edited:
Andy, its an earthing conductor that needs fitting by BG. there is also a lack of protective bonding but imo im competent to be able to run the cable under the floorboards and clamp onto pipework and before anyone says it, yes I do have test equipment
 

Reply to no earthing or bonding conductors in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
Replies
5
Views
2K
What are the regulations requirements on Earth bonding ? I am currently planning a 1st fix re wire I have the following setup Gas Meter...
Replies
3
Views
2K
Hi forum members, I hope someone can assist with my enquiry. I have been advised that to comply with BS7671 Reg 132.16 my solar and battery...
Replies
5
Views
2K
Hi I have a 1st fix domestic install on the go and need to leave a socket for other trades to use after me. There is no main bonding at the...
Replies
7
Views
831
We had our gas disconnected last week and the meter removed. We need to start removing the redundant gas pipes in inside the property. There is...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock