Discuss no end to end reading for r1 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
0
Hi All,
Had a weird one this morning during an EICR.
Testing a ring final circuit in a 2 bed flat… kitchen was on a separate ring. With only the 32A MCB on, I identified 8 sockets on the circuit. Set up for dead testing… r1 end to end - open circuit.
rn - 0.35, r2 - 0.57.
Opened up the 8 sockets… no loose conections or signs of corrosion, however, the ring is wired in pre 2004 red & black… one socket in main bedroom has one leg black and red, the other is brown and blue. The other end of this brown and blue is nowhere to be seen.
With one leg of the ring in the MCB, all sockets have power… swap legs.. all have power.
Decided to try cross connect on r1r2 and got between a low of 0.23 and high of 0.27 for R1+R2.
There aren’t any blank plates, plastered patches from old sockets of jbs to be seen so I’m really confused as to what is going on as at the board I dont seem to have a ring but around the sockets I do.
Thanks in advance for any thoughts given.
 
Seems peculiar r1 open circuit if the sockets are all ok no loose connections & cables are present, looks like a junction connection somewhere hidden 😎
 
Sounds like the brown and blue goes to a junction box or to another socket/FCU etc (that is hidden).
Or, you have a break in the actual line conductor, between sockets.
You'll need to split the ring and narrow down the fault to between 2 sockets. If the fault is between 2 sockets you'll need to have a good understanding of the actual ring layout, so that you can determine which 2 sockets it is between.
I would be making the client aware that this could take a while. Then, slowly and calmly work out the layout of the ring.

There are times when the MCB can be reduced to a 16A or 20A to at least make the situation safe. I wouldn't be doing that in this case as you have continuity with the neutrals meaning there is a line conductor floating around somewhere which could make contact with something.
 
Sounds like the brown and blue goes to a junction box or to another socket/FCU etc (that is hidden).
Or, you have a break in the actual line conductor, between sockets.
You'll need to split the ring and narrow down the fault to between 2 sockets. If the fault is between 2 sockets you'll need to have a good understanding of the actual ring layout, so that you can determine which 2 sockets it is between.
I would be making the client aware that this could take a while. Then, slowly and calmly work out the layout of the ring.

There are times when the MCB can be reduced to a 16A or 20A to at least make the situation safe. I wouldn't be doing that in this case as you have continuity with the neutrals meaning there is a line conductor floating around somewhere which could make contact with something.
Thanks for your reply.
Its certainly going to take some time, especially when there are no visible patches of old jb’s or fcu’s.
I definitely dont want to split the ring into radials when there is a rogue line conductor lurking in the shadows.
 
Just using a plug in tester. I had the faceplates off the wall to check for loose connections during dead testing but didnt power up again with them off.
Did you ever find the fault?
We like updates 😀
 

Reply to no end to end reading for r1 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all EICR today on a ground floor flat .. 1 issue .. At the consumer unit there was a 1mm core with its yellow (sleeved brown) in a 20A radial...
Replies
20
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
306
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock