Do you agree that we only should be working dead when establishing the Zs for final circuits other than socket outlet circuits? That is, don't use the line, neutral and earth probes of the E/L tester except for Ze and Ipsc. Simply add R1+R2 to Ze.
 
A calculated Zs is only theoretical and can be different from a measured Zs, so IMO Zs should be measured unless it really will be dangerous (eg require dismantling live equipment). You can get ES and BC adaptors for light fittings and putting probes on live FCU terminals is hardly 'dicing with death'.
 
Absolutely not. Always test Zs on all circuits how else would you know your circuit complies with the values for maximum permitted Zs. Calculations do not allow for high impedances through some MCB's, RCD's etc.
 
Health and Safety gone mad these days, if you follow the book then Les you're probably correct...no live testing where possible. However, have to agree with Archy and Adam on this one...a measured Zs is far better on the cert than a theoretical one IMO. I think it is acceptable to add R1+R2+Ze for every circuit if you want, but i personally prefer a measured value when/where possible.
 
I won't answer your question directly because I understand my favourite scam suggest what you say

I will however say that once upon a time Electricians were taught to work with electricty,now make of that statemnt what you will

One clue I will reveal,live working focuses my respect if not any avoidance fears
 
Absolutely not. Always test Zs on all circuits how else would you know your circuit complies with the values for maximum permitted Zs. Calculations do not allow for high impedances through some MCB's, RCD's etc.

Completley agree. I think though, that if your theoretical Zs complies it's fine...which is stupid. Theres an apprentice, that used to do abit with me - now with another sparky i know, and apparantly on the 2395 testing and inspection practical exam they wouldn't allow any live testing of the circuits...all measured, and this was fine by them.
 
New posts

Reply to No live testing except where it's a must in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
827
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
919
Hi forum, A question about R1+R2 testing. I’m testing a lighting circuit. It’s an old circuit with old colours. In the control panel feeding the...
Replies
7
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock