Discuss Notifying DNO for first EV install in the Electric Vehicles Advice Forum area at ElectriciansForums.net

Reaction score
39
Hi,

So I plan on installing my first EV charger soon. What's the usual route. Do I notify the DNO and sit and wait for approval or is there a shortcut? What are most electricians doing? I've met a couple who are claiming to be 'banging out' EV chargers but that doesn't really chime well with 'sitting and waiting' for approval. Are many people installing EV chargers and skipping approval altogether?

Thanks

Spynage
 
You must "Apply to Connect" if the maximum demand is above 60A/phase. If it doesn't exceed 60A/phase then you can use the "Connect & Notify". When I have needed to "Apply to Connect" there has been no real hassle dealing with the DNO here. Can't comment on other DNOs though.
 
Is notifying still strictly required?

If joe bloggs can buy a charger from screwfix and knock it in himself, is there still a need?

They all seem to have PEN fault detection and some sort of load management… so is it just so the DNO know beforehand when their infrastructure is going into meltdown?
 
Is notifying still strictly required?

If joe bloggs can buy a charger from screwfix and knock it in himself, is there still a need?

They all seem to have PEN fault detection and some sort of load management… so is it just so the DNO know beforehand when their infrastructure is going into meltdown?
Yes it's legally required.
 
I understand its so the DNO's can plan future work if there's a lot of EV charge points in one area.. They may need to increase capacity....

But for the minimum non-granny chargers? the 7kW or so?

They surely all come with load management now... so they can never reach 60A without some throttling.
 
I understand its so the DNO's can plan future work if there's a lot of EV charge points in one area.. They may need to increase capacity....

But for the minimum non-granny chargers? the 7kW or so?

They surely all come with load management now... so they can never reach 60A without some throttling.
Yes, but they still need to know how many are in use in the area in order to ensure that the infrastructure is capable. It's not like every installation drawing 60A/phase is no problem for the DNO.
 
I’m convinced.

But I bet there’s more installed without notification than those mentioned in #7
Yes correct and the dno are moving on this... all those ozev funded installs have been shared with the dno now. SSEN are cross checking and writing to owners asking who fitted etc and requiring retrospective notifications. causing a right lot of work for them with cut out changes and can if they wish order it be disconnected
 

Reply to Notifying DNO for first EV install in the Electric Vehicles Advice Forum area at ElectriciansForums.net

Similar Threads

On another forum for general EV chat this question comes up all the time. It's very common to install a charger taking the supply direct from the...
Replies
14
Views
2K
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
Hi all Just about to carry out my first EV charger install at the end of the month and im filling out the DNO notification form Im just stuck on...
Replies
11
Views
4K
Hi everyone, looking for some advice or knowledge on DNO approval. I’ve gone to sign up for export with Octopus. On the application form they’ve...
Replies
2
Views
1K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
442

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock